Loc: Titirangi, Akld, New Zealand
About 2 weeks ago we had a buch holtz alarm at T1 tapchanger in our Laingholm substation.
This is situated in the Western suburbs of Auckland NZ.
A bank of 2 transformers of 7.5 MVA supply Laingholm, Huia and Waitipu.

After investigating we found burnt and heavily pitted contacts at the TCOL ( Tap Changer On Load ).
This is the first time in over 40 years these have been serviced for contact renewal.

Photo's are in the Electrical photo galleria.

Regards from Raymond
_________________________
The product of rotation, excitation and flux produces electricty.
Top
Test Equipment:
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement
Large Selection of Test Equipment For Electrical, HVAC, Test & Measurement

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 84 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals