ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 16
Recent Posts
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
Dining room plugs
by watersparkfalls. 03/21/17 10:31 PM
TRUE POWER
by jraef. 03/21/17 09:13 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,394 Are you busy
166,113 Re: Forum
160,572 Need opinion
Who's Online Now
0 registered members (), 55 guests, and 14 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#17772 - 12/02/02 07:25 PM Walk in Refrigerated Building  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 812
NC
I've got a job wiring a refrigerated walk in building. The Building is approx. 40 ft. X 12ft. It has 2 3 phase outside compressors (240 volt) and 2 1 phase evaporators inside with 3 fans each, and also I'm to wire 120 volt circuit for lights and door heater. I already have a 200 amp. 3 phase 30 circuit pole service that was erected for freezer trucks to plug into. As long as I put the required disconnects for the compressors and evaporators etc., can I not just pull straight from the existing service to the building via junction box etc. providing all the right sizing and overcurrent protection and not have to set another panel on the building itself?? I think I'm right but want to see if I might be missing something per Code. Since the service is not attached to the building, does this present a problem? The existing service is only about 12 ft. from where the building is to be located. The existing service is mounted on 2 X 6 treated lumber that is attached to 2 4X4's ( treated also ). This will be about the same scenario as a mobile home service.. Thanks for your input..... [Linked Image]


Work Gear for Electricians and the Trades

#17773 - 12/02/02 08:46 PM Re: Walk in Refrigerated Building  
mj  Offline
Member
Joined: Jun 2002
Posts: 186
meriidian, ms
sounds good to me, i would double ck the bonding requirments. otherwise , i would wire it the same way as you proposed.


#17774 - 12/02/02 10:20 PM Re: Walk in Refrigerated Building  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
Sparkync,

This might be a bit off, however do you think an emergency light might be required? If this is a total walk in building, and if the power goes out, you might need the emergency light to find your way out of there.

HArold


#17775 - 12/02/02 11:04 PM Re: Walk in Refrigerated Building  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
I think that this is a second building fed from a common service and that 225.30, .31, and .32 require a disconnect at the building unless you can meet exception #1 to 225.32.
Don


Don(resqcapt19)

#17776 - 12/02/02 11:34 PM Re: Walk in Refrigerated Building  
The Watt Doctor  Offline
Member
Joined: Dec 2001
Posts: 435
Mont Belvieu, TX
I would consider the following:
1. If you size a feeder, run it from the existing service to the walk in building, set a panel, or gutter, and run your branch circuits from the panel, or tap the gutter, you will (as long as the panel has a main, and you set OCP at the gutter) effectively eliminate the situation that Don has pointed out above. I wouldn't take what Don says lightly, he, from what I've seen, "knows his stuff".
2. Doing it this way will allow the building to be moved in the future by disconnecting the feeder, and "hitting" it with a new feed at it's new location. It makes the building a "self contained" unit.
3. Unless you run the branch circuits from the existing service in separate conduits, you will have to derate the wire.
4. Remember your "within sight of" rules for disconnects.

"Walk in" through the "out" door,
Doc


The Watt Doctor
Altura Cogen
Channelview, TX

#17777 - 12/04/02 09:30 AM Re: Walk in Refrigerated Building  
sparkync  Offline
Member
Joined: Oct 2002
Posts: 812
NC
Don Thanks for the information. You were exactly right about the sub panel... checked with the AHJ .. said the same... like to get some of my facts together before going to them though [Linked Image] That was my first thoughts, then I when I really started thinking, is where I missed it [Linked Image] Thanks again,,Doc was right, you know your stuff [Linked Image]



Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 6,799
Joined: April 2002
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.7752 MB (Peak: 0.9183 MB) Zlib enabled. Server Time: 2017-03-25 07:50:51 UTC