#17768 - 12/02/02 02:12 PM Gutters
Electra Offline
Member
Registered: 07/29/02
Posts: 38
Loc: Portland, Oregon, USA
Can anyone tell me the difference between an auxiliary gutter and a metal wireway. The only difference I see is that an auxiliary gutter cannot be longer than 30 feet and it allowed to have busbar in it. Is it the busbar that really distinguishes the two? Otherwise, why wouldn't we just call everything a wireway instead of a gutter?

Thanks
Top
Work Gear for Electricians and the Trades
#17769 - 12/03/02 09:03 AM Re: Gutters
mountainman Offline
Member
Registered: 01/29/02
Posts: 54
Loc: Richmond Va. U.S.A.
If you look at art. 366.2, and art. 376.2 you will see the difference. Auxiliary gutters are for augmenting wire space at " meter centers, distribution centers, and simular points of wiring systems." Thats why it is limited to 30 feet. Metal wireways can be used for all other applications and has no length restrictions. Hope this helps and have a happy and safe holiday. Mountainman
Top
#17770 - 12/03/02 09:24 AM Re: Gutters
Electra Offline
Member
Registered: 07/29/02
Posts: 38
Loc: Portland, Oregon, USA
This is still not very clear to me. Let's say for example that I have a gutter/wireway above a couple of panels with chases. It does not extend 30' past the panels. Does it matter whether I call it an auxiliary gutter or a wireway, because it seems like either one would apply in this case?
Top
#17771 - 12/03/02 10:11 AM Re: Gutters
mountainman Offline
Member
Registered: 01/29/02
Posts: 54
Loc: Richmond Va. U.S.A.
An auxiliary gutter would be and addition to the wire space for equipment. Thats why the code allows busbars in them. Wireways are not restricted to just equipment or lengths. Auxiliary gutters can extend 30' from the equipment. Wireways you can install any amount of length and are not restricted to just service equipment and the like. Even though both are physically the same piece of product, the definition is the key. Wireways you can install anywere on the job, but auxiliary gutter would for all practicle porposes would be in your equipment rooms.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 95 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals