#177674 - 05/09/08 11:43 AM Cable derating for transformer rise
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
I recieved this information for a NEMA 4 dry-type transformer I required for a particular application, and was concerned the enclosure will end up essentially being an enclosed box that will just bake my cables.

Quote:
[Our company] designs enclosed transformers to have a maximum enclosure temperature of 65C above ambient for readily accessible parts and a maximum temperature rise of 80C for not readily accessible parts per IEEE 57.12.01.


If 115° and 150°C rise and hotter are common ratings for transformers, how in the world is this reconciled with 90°C rated cables?

I'm having difficulty finding any solid information about this. Am I worried over nothing, will the cables wick away the heat fast enough that it's not an issue? I don't mind derating cabling, but it's difficult to derate a 90C cable for 120C ambient conditions. If I go strictly by NEC, I know I can ignore this because it's less than 2' at the end of the cable, but it still worries the hell out of me. What's the standard way to terminate to a NEMA 4 transformer?
Top
Work Gear for Electricians and the Trades

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals