#177597 - 05/08/08 06:11 AM 70-E & utility companys
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
By reading 70-E there not really covered by this even when working on HV switchgear am I right.
Top
Arc Flash PPE Clothing, LOTO & Insulated Tools
#177603 - 05/08/08 07:39 AM Re: 70-E & utility companys [Re: Yoopersup]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
I am not sure what you mean by you post. 70E is just a standand that was written to "clearify" OSHA requirements. 70E is applicable if adapted by your employer.

In other news, Something I have been wanting to ask you. Going by your user name, where abouts in the U.P. are you Located? I was born and raised as a "Troll". (Michigan humor).
_________________________
"Live Awesome!" - Kevin Carosa
Top
#177629 - 05/08/08 04:33 PM Re: 70-E & utility companys [Re: sparkyinak]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
I forgot to put before the Post Utility Companys.
North of the bridge about 200 miles.
Top
#177741 - 05/11/08 06:45 AM Re: 70-E & utility companys [Re: Yoopersup]
Zog Offline
Member
Registered: 09/13/05
Posts: 120
Loc: Charlotte, NC
Utilities follow NESC, they have been able to dodge 70E for while now but are in the process of adapting many of the 70E rules. They also follow 1910.269 which has many of the same SWP's.

The only thing the 70E brings is the are flash calcs and PPE requirements. The tables only apply up to 38kV and the calcs dont work either, so really they ARE following the 70E, at least the parts that apply.

As far as PPE, linemen have been wearing arc resistant materials for years, but in the substations (Indoor, metal clad switchgear) the current rules the utilities follow are not good enough to protect workers, this is where they SHOULD be following 70E and this is where most of the upcoming NESC changes will apply.

The thing is, an arc flash at 72kV in open air is nothing compared to one at 480V in a cubic box with high available fault currents and a lonfg clearing time like what is found on nearly every 480V substation out there.

I hope I answered your question, if not, please ask a more specific question.
_________________________
MV/HV Testing Specialist, "BKRMAN"
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 20 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals