The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 257 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#177543 - 05/06/08 03:47 PM underground conductors failed in RMC - Why?
WNYJim Offline
Member

Registered: 06/06/02
Posts: 39
Loc: Rochester, NY, USA
Four years ago I had a call for a free standing meter station that had lost one hot leg.
The 100A supply came down a pole, underground (about 10') and up to the meter channel.
Pulled the wires out and found one of the aluminum conductors was completely separated. The insulation showed no sign of failure (other than some melting right at the break) and the conductor had some oxidation at each open end.
Pulled in new URD and all was fine.
This spring I got a call that it happened again.
So this time the RMC was removed and replaced with PVC.
The break occured in the same spot as before. The conduit was inspected for sharp edges or anything that could have caused this failure.
Just like the first time the wire showed no sign of damage (nicks, cuts, scrapes).
There is very little load on this, it only feeds a 150 watt spot light and a 1/4 HP pump.
The original feed lasted 40 years, the second only 4.
Any ideas?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#177544 - 05/06/08 04:01 PM Re: underground conductors failed in RMC - Why? [Re: WNYJim]
LK Offline

Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
We found like that, turned out the homes were moving away from the street, the homes were built on steep hills, and were falling away from the road, pulling the wire apart.

Top
#177545 - 05/06/08 04:29 PM Re: underground conductors failed in RMC - Why? [Re: LK]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Is this in an area that has frost and is the conduit below the frost line? I have seen conductors damaged when the water in the raceway freezes and crushes the insulation.
_________________________
Don(resqcapt19)

Top
#177546 - 05/06/08 04:31 PM Re: underground conductors failed in RMC - Why? [Re: LK]
WNYJim Offline
Member

Registered: 06/06/02
Posts: 39
Loc: Rochester, NY, USA
The break was in the section underground.
The soil is all sand and no strain was found on the wires.
The wires had a nice loop in the meter channel and on the pole there was plenty of slack.
I'm stumped!

Top
#177548 - 05/06/08 05:40 PM Re: underground conductors failed in RMC - Why? [Re: WNYJim]
walrus Offline
Member

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
Frost can play havoc with a pipe full of water?? What about road salt?? and a knick in the insulation


Edited by walrus (05/06/08 05:41 PM)

Top
#177553 - 05/07/08 02:54 AM Re: underground conductors failed in RMC - Why? [Re: walrus]
WNYJim Offline
Member

Registered: 06/06/02
Posts: 39
Loc: Rochester, NY, USA
It could have been frost but we didn't see any damage to the other wires.
This is located about 100ft from the road and the coduit was in good shape.

Top