The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (LongRunner, Tjia1981), 178 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#177421 - 05/02/08 05:48 AM 2500 KVA 480/277 secondary Transformer conduit & w
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Thur experience for Cost (Material & Labor) what have you found to be the most cost effective combination of pipe & wire??? Pvc Sch. 40 with Alum or Copper . I;m looking for 3000 amps. Another words 500 mcm , 750, 1000 copper or alum.
4 wires in a conduit. Useing 310.16 75C & 110.14c for terms.
Yoopers
Also mostly 480 volt loads so Neutral can be 12 1/2 percent of phase conductors right.

Top
2014 / 2011 NEC & Related Books and Study Guides
#177423 - 05/02/08 07:19 AM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: Yoopersup]
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Didn't you already ask this question back in February?

Top
#177431 - 05/02/08 10:09 AM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: electure]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
I'd take a look at bus duct for that size feeder.
_________________________
Don(resqcapt19)

Top
#177438 - 05/02/08 02:56 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: resqcapt19]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
One I posted in Feb was a bit different , Just wondering thur experience which way worked out better.never to proud to learn. Right

Top
#177523 - 05/05/08 05:02 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: Yoopersup]
Tesla Offline
Member

Registered: 06/16/04
Posts: 1280
Loc: Sacramento, CA
At 3000 Amps your 'window' becomes restrictive, you'll need to stuff 400 Amps in each of eight pipes. That means that you might be forced to go with copper in schedule 40 PVC.

By comparison, bus duct can be had at 3000 Amps in AL.

The shorter path and cheaper conductor makes bus duct a serious competitor.
_________________________
Tesla

Top
#177525 - 05/05/08 05:59 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: Tesla]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
Another consideration with bus duct is the difference in labor hours. Slap up 1 10' length of bus duct and you're done with 10' of feed. For 10' of conduit you still have to pull and terminate the wires...PLUS you have multiple sets of everything.
_________________________
Ghost307

Top
#177571 - 05/07/08 05:01 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: ghost307]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
Cost of Buss Duct custom made otta this world .

Top
#177583 - 05/07/08 08:35 PM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: Yoopersup]
George Little Offline
Member

Registered: 01/18/04
Posts: 1492
Loc: Michigan USA
Ernie- You've left out some details (as usual) and I wonder if the question factors in the grounding conductor? With metal raceway - no ground wire- with non-metallic you will need a ground wire- since this is not service. Right? Wrong?
_________________________
George Little

Top
#177590 - 05/08/08 04:17 AM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: George Little]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
How long is the total run? You have to watch out for the length difference with parallel runs.
_________________________
Don(resqcapt19)

Top
#177594 - 05/08/08 05:52 AM Re: 2500 KVA 480/277 secondary Transformer conduit & w [Re: resqcapt19]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
George
Service conduits from utility Co, transformer to Service gear that means NO GROUND WIRE.
Total run is Aprox. 40feet and yes I know about requrements of Parrell runs.
Buss 90's if you've ever installed then cost a bundle as well as regular buss. But I agree worth a price compaireson.


Edited by Yoopersup (05/08/08 05:59 AM)