The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 301 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#177290 - 04/28/08 06:40 AM And yet another Sub question
Reel-Break Offline

Registered: 04/04/02
Posts: 179
Loc: nc
I`m working with a new contractor whom insist I put a main in the house. I have a 200a meter main out side and have installed a 100 main lug inside with the 100 ocp out in the metermain.Guess I`m not going to find in exact words this is legal I showed him I had ocp for the panel to protect everything has someone got some Code references I can shoot at him.
Wouldn`t 408.36 cover it?

2014 / 2011 NEC & Related Books and Study Guides
#177294 - 04/28/08 07:11 AM Re: And yet another Sub question [Re: Reel-Break]
sparkyinak Offline

Registered: 07/08/07
Posts: 1288
Loc: Alaska
I am not sure what you are shooting at with 408.36. The main is the panel is not required per NEC. I doubt that it is a local ordinance since you are saying it is not required. If the contractor or the customer is going to pay for it, give them what they want. It may just give them a piece of mind. If you have already ordered parts, tell them how much it is going to cost for the change. Check you project specs. if the project came with them.
"Live Awesome!" - Kevin Carosa

#177298 - 04/28/08 09:05 AM Re: And yet another Sub question [Re: sparkyinak]
BPHgravity Offline

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
Yes, 408.36 is the correct section to cite in regard to NOT requiring a "main" breaker inside a panelboard supplied by a feeder with proper overcurrent protection.
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

#177328 - 04/29/08 08:48 AM Re: And yet another Sub question [Re: BPHgravity]
JValdes Offline

Registered: 06/03/07
Posts: 308
Loc: South Carolina
Glad I looked at this thread. I have always understood that a sub panel in an unattached structure requires a main breaker and one or more electrodes, in addition to the main breaker for the feeders.
Is this thread concerning a main service and that is why I do not understand using a lug panel is a violation?

#177329 - 04/29/08 08:58 AM Re: And yet another Sub question [Re: JValdes]
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
If you go to a second building you need another disconnect but I understand this as all being in or on the same building. This is not that unusual on a piling house where they have a service disconnect at ground level and a lighting and appliance board up in the dwelling.
Greg Fretwell

#177332 - 04/29/08 09:26 AM Re: And yet another Sub question [Re: JValdes]
SteveFehr Offline

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
In this case, he's got the OCP/service disconnect as a separate breaker, and so does not need a main breaker on his panel.

#177433 - 05/02/08 12:31 PM Re: And yet another Sub question [Re: SteveFehr]
Reel-Break Offline

Registered: 04/04/02
Posts: 179
Loc: nc
Yes this is correct. Small cracker box house just set metermain outside to catch the heat and hvac 100 amp sub 20 space in the house. But the main reason for the metermain is the fact of where the panel was located and poco entrance.I coundn`t go back to back.


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals