The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#177290 - 04/28/08 06:40 AM And yet another Sub question
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
I`m working with a new contractor whom insist I put a main in the house. I have a 200a meter main out side and have installed a 100 main lug inside with the 100 ocp out in the metermain.Guess I`m not going to find in exact words this is legal I showed him I had ocp for the panel to protect everything has someone got some Code references I can shoot at him.
Wouldn`t 408.36 cover it?

Top
2014 / 2011 NEC & Related Books and Study Guides
#177294 - 04/28/08 07:11 AM Re: And yet another Sub question [Re: Reel-Break]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1295
Loc: Alaska
I am not sure what you are shooting at with 408.36. The main is the panel is not required per NEC. I doubt that it is a local ordinance since you are saying it is not required. If the contractor or the customer is going to pay for it, give them what they want. It may just give them a piece of mind. If you have already ordered parts, tell them how much it is going to cost for the change. Check you project specs. if the project came with them.
_________________________
"Live Awesome!" - Kevin Carosa

Top
#177298 - 04/28/08 09:05 AM Re: And yet another Sub question [Re: sparkyinak]
BPHgravity Offline
Member

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
Yes, 408.36 is the correct section to cite in regard to NOT requiring a "main" breaker inside a panelboard supplied by a feeder with proper overcurrent protection.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

Top
#177328 - 04/29/08 08:48 AM Re: And yet another Sub question [Re: BPHgravity]
JValdes Offline
Member

Registered: 06/03/07
Posts: 308
Loc: South Carolina
Glad I looked at this thread. I have always understood that a sub panel in an unattached structure requires a main breaker and one or more electrodes, in addition to the main breaker for the feeders.
Is this thread concerning a main service and that is why I do not understand using a lug panel is a violation?
Thanks....john

Top
#177329 - 04/29/08 08:58 AM Re: And yet another Sub question [Re: JValdes]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
If you go to a second building you need another disconnect but I understand this as all being in or on the same building. This is not that unusual on a piling house where they have a service disconnect at ground level and a lighting and appliance board up in the dwelling.
_________________________
Greg Fretwell

Top
#177332 - 04/29/08 09:26 AM Re: And yet another Sub question [Re: JValdes]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
In this case, he's got the OCP/service disconnect as a separate breaker, and so does not need a main breaker on his panel.

Top
#177433 - 05/02/08 12:31 PM Re: And yet another Sub question [Re: SteveFehr]
Reel-Break Offline
Member

Registered: 04/04/02
Posts: 179
Loc: nc
Yes this is correct. Small cracker box house just set metermain outside to catch the heat and hvac 100 amp sub 20 space in the house. But the main reason for the metermain is the fact of where the panel was located and poco entrance.I coundn`t go back to back.

Top