The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 18
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 245 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#177101 - 04/22/08 03:05 AM Voltage Drop Calcs.
Angel_Electric Offline
Member

Registered: 06/03/07
Posts: 21
Loc: Fl.
I'm Studying a book Called Electrical Wiring Commerial 13Th. Edition.I've run into a formula for voltage drop.The variable (K)is unknown to me and the book does not reference where, why or how its use has derived.The formula is VD=2xKxDxI/Cm. Does anyone Know of an explicit reference for this (K). Thanx

Top
#177103 - 04/22/08 04:09 AM Re: Voltage Drop Calcs. [Re: Angel_Electric]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
VD=2xKxDxI/Cm

I= Current
2= round trip loss (you'd use 1x if it was a balanced wye circuit)
KxD/Cm represents the resistance of this wire.

Voltage Drop = 2x Current x Resistance

D=length of wire
K/Cm=resistance per unit length.

K is the unit resistance of copper per circular mil
Cm is circular mills of the conductor. (roughly 2.8 Ohms/kcmil/100 feet DC) This equation is only accurate for DC. You can approximate AC (K is roughly 1.3 for AC), but it varies by cable size due to skin resistance and isn't terribly accurate.

This entire value (the resistance per unit length) can simply be looked up in NEC Tables 8 & 9, though. Really, you should also be adjusting it forpower factor and the type of conduit it's in and wire temperature, too, but usually if you have to go into that much detail, you should be upsizing anyhow.

Top
#198935 - 02/07/11 10:43 PM Re: Voltage Drop Calcs. [Re: Angel_Electric]
nercGerald Offline
Member

Registered: 02/05/11
Posts: 15
Loc: North Pole, Alaska
Try my latest presentation based on the NEC at:
http://www.electrician2.com/voltdrophtml/frame.htm

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals