The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
gfretwell 11
sparkyinak 10
ghost307 10
Trumpy 8
Who's Online
1 registered (HotLine1), 299 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#1770 - 05/29/01 06:20 PM voltage present when power is turned off???
smokey Offline
Member

Registered: 04/06/01
Posts: 42
Loc: cctxusa
out on a job once i remember sticking my meter to check for voltage and all i was reading was 6.6v between ungrounded conductor(hot) and the grounded conductor (neutral) on the receptacle with the breaker feeding the circuit turned off.. where was this mysterious voltage coming from??? could it have been a backfeed of some sort???

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#1771 - 05/29/01 06:22 PM Re: voltage present when power is turned off???
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
smokey;
it's probably induction, you could flip breakers until the culprit was found.

Top
#1772 - 05/30/01 07:00 PM Re: voltage present when power is turned off???
smokey Offline
Member

Registered: 04/06/01
Posts: 42
Loc: cctxusa
thanks sparky

Top
#1773 - 06/01/01 04:32 AM Re: voltage present when power is turned off???
electure Offline


Member

Registered: 12/24/00
Posts: 4227
Loc: Fullerton, CA USA
I still carry my old solenoid Wiggy with me, as well as my digital tester. The Wiggy puts enough load on the wire being tested to zero out these induced readings (try them both at once = 0). You can get some pretty high readings w/ the digital on long homeruns @ 277/480.

Top
#1774 - 06/01/01 10:18 AM Re: voltage present when power is turned off???
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2342
Loc: West Virginia
Sans Wiggy, I have put a resistor (light bulb on a pig tail) between the same two points and then measure the voltage. The connection to ground tends to "bond" any stray voltage...I think. If it reads 0 volts set up this way, then no worries...if the bulb burns, you have a short. I'm sure the wattage of the bulb comes into play here too for any resisted shorts that would complicate the issue.

I'm asking opinions here rather than suggesting this method. It's sort of a "poor man's" troubleshooting trick, but I'd like to know all the "druthers" involved... Any comments?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#1775 - 06/01/01 05:20 PM Re: voltage present when power is turned off???
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Look for the report at www.nema.org

[This message has been edited by Joe Tedesco (edited 01-09-2003).]
_________________________
Joe Tedesco, NEC Consultant

Top