The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 261 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#176186 - 03/24/08 09:51 AM colour of loomex
wacked Offline
Member

Registered: 12/19/06
Posts: 33
I was talking to a friend who recently wired his own house. He said that the code stated that there was a requirement to have red loomex for heating circuits, blue for bedrooms, yellow for lights etc. He lives in a different city.... I recently wired my brothers new house with your basic white loomex and had no problem with the inspector. I checked the BC electrical code/bulletins/directives and found nothing on this. Does anybody have any comments on this? Maybe there are local rules with certain inspectors?

Top
2014 / 2011 NEC & Related Books and Study Guides
#176187 - 03/24/08 10:29 AM Re: colour of loomex [Re: wacked]
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
 Originally Posted By: wacked
I was talking to a friend who recently wired his own house. He said that the code stated that there was a requirement to have red loomex for heating circuits, blue for bedrooms, yellow for lights etc. He lives in a different city.... I recently wired my brothers new house with your basic white loomex and had no problem with the inspector. I checked the BC electrical code/bulletins/directives and found nothing on this. Does anybody have any comments on this? Maybe there are local rules with certain inspectors?

There is no code rules stating what color you have to use.
_________________________
Never trust an electrician with no eyebrows!!

Top
#176188 - 03/24/08 03:56 PM Re: colour of loomex [Re: mr_electrician]
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
AFAIK there is no code issues the colouring is just there to provide a means to identify conductor size, voltage and circuit type in a round about way for when the inspector comes.. I have heard of houses where the general lighting and receptacles were done in blue and the AFCI's in white with no problem BUT I almost got 'dinged once for using a piece of 12/2 yellow ( black and white conductors) for a 240V electric heater instead of the 12/2 red ( black and red conductor), even though I identified the white wire as a hot.

A.D
A.D

Top
#176201 - 03/25/08 04:21 AM Re: colour of loomex [Re: Rewired]
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
 Originally Posted By: Rewired
BUT I almost got 'dinged once for using a piece of 12/2 yellow ( black and white conductors) for a 240V electric heater instead of the 12/2 red ( black and red conductor), even though I identified the white wire as a hot.

A.D
A.D

The inspector probably mentioned this because you cannot tape any wires under a certain size.(if thats how you indentified it) Just like you can't use 3 wire BX for a isolated ground anymore. You have to use the AC90 with a bare bond wire and insulated green wire.
_________________________
Never trust an electrician with no eyebrows!!

Top
#176217 - 03/25/08 05:30 PM Re: colour of loomex [Re: mr_electrician]
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
No size limitation for rendering the identified conductor unidentifiable when using loomex or bx.

Top
#176261 - 03/27/08 02:40 PM Re: colour of loomex [Re: RobbieD]
Rick Kelly Offline
Member

Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
That is correct... take a look at 4-034(1).

Top
#176288 - 03/28/08 04:08 PM Re: colour of loomex [Re: Rick Kelly]
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
Mr_Electrician:
The reason I was given is " Someone may mistake it for a 120V circuit and tap into it".. A bit far fetched if you ask me, and I have seen tons of 240V installs that have been done with regular 2 conductor ( black and white ) romex with no problems... I wonder what would have been said if I happened to have used AC-90, how that would have played out.

Speaking of AC-90, I have worked with the "iso ground" AC-90 before. I was told it was because of too many people connecting the red to a breaker and not to ground, making for a dangerous situation..
I am not sure and I will check, but I *think* that regular 3-conductor AC-90 may be used as long as the red conductor is sleeved with green heat-shrink tubing and NOT taped, and done in every box the cable is spliced or terminated at..

A.D

Top
#176307 - 03/29/08 04:39 AM Re: colour of loomex [Re: Rewired]
Sandro Offline
Member

Registered: 12/30/01
Posts: 449
Loc: Stoney Creek, ON, Canada
There was an ESA bulletin on this. Ever since iso wire became available, we can longer use regular 3 wire BX as iso ground on new installations. Some inspectors may close an eye, but in the eyes of the code, it is a violation.


Top
#176310 - 03/29/08 07:47 AM Re: colour of loomex [Re: Sandro]
Sixer Offline
Member

Registered: 08/08/05
Posts: 264
Loc: Canada
 Originally Posted By: Sandro
Ever since iso wire became available, we can longer use regular 3 wire BX as iso ground on new installations. Some inspectors may close an eye, but in the eyes of the code, it is a violation.


Our inspector told me that we can't use regular 3 wire BX for isolated grounds also, but I'm unable to find a rule on this. The closest thing I can find is 10-906(9).
_________________________
Sixer

"Will it be cheaper if I drill the holes for you?"

Top
#176311 - 03/29/08 08:40 AM Re: colour of loomex [Re: Sixer]
Rick Kelly Offline
Member

Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
Rule 24-104, in the "Patient Care" section, mandates the use of a insulated bonding conductor, unless insulated by way of a non conductive raceway or by the construction of the cable containg the conductor.

Rule 4-036(1) mandates that a insulated grounding or bonding conductor be green or green with a yellow stripe.

Using any other color as a bonding or grounding conductor, is permitted only if the conductor is a #2 or larger and if it is permanetly re-identified as required by 4-036(1b) and "no", tape is not adequate in my books.


Edited by Rick Kelly (03/29/08 08:41 AM)