#175951 - 03/15/08 04:31 PM Cable Tray Derateing Of Parallel 500 kcmil conduc
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
392.8 (d) conductors in cable tay Paralleled Shall be Grouped.
392.11 (B)(2) single conductors 1/0 to 500 kcmil grouped shall be derated at 65% per tables 310.17 -310.18 .
tray no cover free air copper 500 kcmil=(700amp at 90%c) (for derateing only)x 65% = 455 amps per group.

Unless installed with free air space per 392.11 (b)(4)then table 310.20 (500 kcmil=580amps at 90c )

Wanna check my work guys ???
YoopersUp



Top
2017 / 2014 NEC & Related Books and Study Guides
#176283 - 03/28/08 07:04 AM Re: Cable Tray Derateing Of Parallel 500 kcmil conduc [Re: Yoopersup]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
??????????
Nobody does this type of work???
Top
#176285 - 03/28/08 10:25 AM Re: Cable Tray Derateing Of Parallel 500 kcmil conduc [Re: Yoopersup]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
Just use a bigger tray laugh Grouping doesn't mean they have to be bundled, you just need to run the whole group together in a single tray (or parallel trays are OK too, I believe). If you can leave a cable diameter between the 500kcmil cables, you don't need to derate at all. I've often seen them tie-wrap cables to the trays to maintain spacing. Looks cheap with all the tie-wraps (IMHO), but very clean, and is very effective at maintaining spacing.

I really don't see why NEC would specifically disapply 310.15(B)(2) though, it doesn't make sense, and 65% is a HARSH derating. Ask your AHJ, they may be lenient about minimum cable space to avoid derating- I know I sure am on cable spacing in venetilated trays.

Alas, I won't have to worry about this anymore- as of 2008, 708.10(C) specifically prohibits it for my sites, even when the EMI environment will allow open tray. All RMC from now on, I suppose. Maybe the occassionally SCH80 duct bank...


Edited by SteveFehr (03/28/08 10:35 AM)
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals