The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Potseal 7
Who's Online
0 registered (), 300 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#175876 - 03/13/08 02:46 PM Tray Cables into Mcc's termination methods???
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
I;ve seen Chase nipples put into the top of Mcc's (in wireways only) then several Tray cables run into them . I told the conmtractor I didn't feel this was a approved termintation method. I;ve seen Nipples from Mcc's up to the tray (lest them 24inches . But never Chase nipples?? My concern was even thought the nipples open into the wireways it leaves an unprotected opening.YER opinions Please.
YoopersUp

Top
2014 / 2011 NEC & Related Books and Study Guides
#175878 - 03/13/08 03:24 PM Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
I have seen what you describe. The wiring trough area of MCC's (for load conductors) does not provide direct access to any energized parts, I would be more concerned with securing the TC.

Top
#175882 - 03/13/08 04:16 PM Re: Tray Cables into Mcc's termination methods??? [Re: JBD]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
The drop from the tray to the Mcc's is only about 24-36 inches Max.what about 392.8(c)

Top
#175884 - 03/13/08 05:30 PM Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Take a look at 312.5(C) and 314.17(B).
_________________________
Don(resqcapt19)

Top
#175887 - 03/13/08 06:27 PM Re: Tray Cables into Mcc's termination methods??? [Re: resqcapt19]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
But does a MCC come into play in that section??

Top
#175997 - 03/17/08 04:55 PM Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
In my opinion, between Articles 312 and 314, all electrical enclosures are covered.
_________________________
Don(resqcapt19)

Top
#176032 - 03/18/08 03:27 PM Re: Tray Cables into Mcc's termination methods??? [Re: resqcapt19]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
The Scope sections 312.1 & 314.1 says otherwise.

Top
#176121 - 03/20/08 06:04 PM Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
I think that I can stretch the scope of 314 to cover just about any electrical enclosure including MCCs.
_________________________
Don(resqcapt19)

Top
#176144 - 03/21/08 05:25 PM Re: Tray Cables into Mcc's termination methods??? [Re: resqcapt19]
Yoopersup Offline
Member

Registered: 03/04/03
Posts: 826
Loc: Michigan
314 No way. 312 you'd have to use 90.4 and I really think you'd be streaching it. Which one is it a Cabinet(see definitions) Cut out box (No), Meter Socket encloser (No).
So then a MCC must be a Cabinet .
Cabinet (an encloser that is designed for either surface mounting or flush mounting and is provided with a frame ,mat, or trim in which a swinging door or doors are or can be hung. Doesn;t sound like a MCC does it??

Top
#176160 - 03/22/08 08:12 PM Re: Tray Cables into Mcc's termination methods??? [Re: Yoopersup]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The part of the MCC that you run the cables into is used as a pull box.
 Quote:
314.1 Scope
This article covers the installation and use of all boxes and conduit bodies used as outlet, device, junction, or pull boxes, depending on their use, and handhole enclosures.
_________________________
Don(resqcapt19)

Top