The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 295 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#175527 - 03/03/08 03:43 PM Refrig On GFCI Outlet is this a Code issue?
ComputerWizKid Offline
Member

Registered: 09/20/03
Posts: 116
Loc: Connecticut, USA
I was looking at an apartment I'm thinking of moving into and I noticed the refrigerator was plugged into a GFCI outlet. I know compressors can trip GFCIS when they start up and make the food spoil but I want to know if this is a code issue so I can bring it to the managements attention

Thanks
_________________________
Theres always enough room in the junction box.You just need a bigger hammer

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#175528 - 03/03/08 04:10 PM Re: Refrig On GFCI Outlet is this a Code issue? [Re: ComputerWizKid]
BPHgravity Offline
Member

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
No real issue. The code does not prohibit nor require a regrigerator located in a dwelling kitchen to be gfci protected. See 210.52 and 210.8 of the NEC.

In the event the refrigerator trips the gfci repeatedly, it is an indication the refrigerator is not operating properly. The leakage current permitted on appliances should not exceed the threshold of Class A gfci devices (5mA).
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

Top
#175529 - 03/03/08 04:39 PM Re: Refrig On GFCI Outlet is this a Code issue? [Re: BPHgravity]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
The fridge in my tiki bar out by the pool has always been on a GFCI. So far so good.
_________________________
Greg Fretwell

Top
#175532 - 03/03/08 05:59 PM Re: Refrig On GFCI Outlet is this a Code issue? [Re: gfretwell]
Theelectrikid Offline
Member

Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
Fridge and chest freezer in the garage are plugged into one, thing has never tripped. (Except tests, of course.)

Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?

Top
#175534 - 03/03/08 06:30 PM Re: Refrig On GFCI Outlet is this a Code issue? [Re: Theelectrikid]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
They are not required per code but I would avoid it at all possible which is difficult in unfinished garages.

A funny thing happen a couple of years ago. In one on our employee's housing units, the tentants lost a whole freezer full of food because, it turned out that the GFCI was wired wrong for quite a few years. The irony of it was previous occupants did not trip it. The GFCI circuit was part of a multi-wire circuit in which the neutral and one leg fed through the GFCI. It never tripped because they other circuit was never used, there the GFCI circuit was always balanced. When the new occupants were moving in, they used the other circuit creating an unbalance whiched tripped the GFCI. They did not question or even realized the other circuit was not working right (open neutral).
_________________________
"Live Awesome!" - Kevin Carosa

Top
#175549 - 03/04/08 04:26 AM Re: Refrig On GFCI Outlet is this a Code issue? [Re: sparkyinak]
BPHgravity Offline
Member

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
Another issue with gfci protection is that many times, installers will place several receptacle outlets on the load side of the gfci device, be it a breaker or outlet type. Under this configuration, any one appliance may not exceed the 5mA trip setting of the gfci device. However, several appliances operating together may.

This will likely always be a design consideration, but leads one to believe the gfci is malfunctioning, nusiance tripping, or wired incorrectly.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

Top
#175556 - 03/04/08 08:00 AM Re: Refrig On GFCI Outlet is this a Code issue? [Re: BPHgravity]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
 Originally Posted By: BPHgravity
Under this configuration, any one appliance may not exceed the 5mA trip setting of the gfci device. However, several appliances operating together may.

I am not disagreeing with you on this. In my years of experiences, I have never had an issue with GFCI's tripping because of this. I have heard dozens of claims of what causes nescience tripping. I would say 0.1% of claims are truly nescience tripping. The rest on the time, they did thier job. This is providing that the circuit is wired properly.

Do not quote me on this but I do not think that household appliances are allowed a certain current leaking (with the exception of surge protectors). I do not think capacitors are allowed an x amount of leakage. They do in time leak due to age. If a GFCI is tripping, it is 99.9% chance there is a pending problem that should be addressed before it comes a real problem.

Number 1 complaint I get about so called defective GFCI's is, "I plugged my hair dryer in and the GFCI trips. I plug it in a regular outlet and it works fine. The GFCI is broken."

I live in a very wet environment. When installed and used properly, we get many good years of service out of them providing the poor power quality dosen't kill the circuit board first.
_________________________
"Live Awesome!" - Kevin Carosa

Top
#175559 - 03/04/08 08:49 AM Re: Refrig On GFCI Outlet is this a Code issue? [Re: sparkyinak]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Not requiring a fridge/freezer to be on GFCI is not because the fridge/freezer will trip it, but because a GFCI trip elsewhere on the circuit could lead to food spoilage. If any household motor is leaking more than 6ma to ground, it's a problem that should be fixed.

Top
#175565 - 03/04/08 09:50 AM Re: Refrig On GFCI Outlet is this a Code issue? [Re: SteveFehr]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I think old fridges trip GFCIs because of internal compressor shorts. (I know there are spikes on the EGC but my scope pictures didn't come out) That is why the freon always smells "burnt" and why energy usage goes up. A bet an AFCI, even without GF protection, is going to trip too so the 2008 code is going to get a lot of these old appliances into the landfill. I believe the same is going to be true of old washing machines (also notorious GFCI trippers). Buy stock in Whirlpool/GE when this hits.