The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 15
sparky 9
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 226 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#175308 - 02/26/08 04:21 PM Receptacles above drop ceiling ?
derater Offline
Member

Registered: 03/30/02
Posts: 182
Permissible or not ? I'm all resi, and just never paid any attention to this issue. Thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#175309 - 02/26/08 05:35 PM Re: Receptacles above drop ceiling ? [Re: derater]
JBD Offline
Member

Registered: 07/12/01
Posts: 599
Loc: WI, USA
 Originally Posted By: derater
Permissible or not ? I'm all resi, and just never paid any attention to this issue. Thanks


Yes absolutely receptacles are allowed above drop ceilings.

However you may not use them to feed a flexible cord, because 400.8 does not allow flexible cords above ceilings.

Low voltage transformers (wall warts) may be plugged directly into the receptacle if they are Class 2 devices and their output cord is not one of the NEC prohibited flexible cord styles. another use for these receptacles would be for portable/temporary equipment (i.e. work light)that is removed prior to "closing" the ceiling.

Top
#175347 - 02/27/08 06:56 AM Re: Receptacles above drop ceiling ? [Re: JBD]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 876
Loc: Chicago Illinois USA
As long as someone wants me to provide a receptacle above the ceiling for those purposes, I'm fine with it.
But as soon as they say that they want it to plug something into it and leave it (like a condensate return pump), I get antsy. I don't want to be part of their violation of 400.8; I wish that the Code was worded differently...it seems to be trying to fix one problem by addressing a different issue.
_________________________