#175047 - 02/20/08 02:51 PM arc -faults
tomselectrc Offline
Member
Registered: 03/14/04
Posts: 50
Loc: warren mi us
have a attic fan in bedroom, need arc-fault? tried a cutler hammer breaker keeps tripping. attic fan about 30 years old. any suggestions inspector wants arc fault
Top
2017 / 2014 NEC & Related Books and Study Guides
#175048 - 02/20/08 03:32 PM Re: arc -faults [Re: tomselectrc]
leland Offline
Member
Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
120V 15-20A, in a bedroom, Yes AFCI.
New fan.
Howed the inspector get involved? Remodel?
Top
#175049 - 02/20/08 03:41 PM Re: arc -faults [Re: leland]
Tom Offline
Member
Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Maybe it is time for a new fan. AFCI's include ground fault protection which trips at about 30ma. The fan that old could have defective insulation which would trip the AFCI. Another thing to investigate, if you haven't already, is the possibility of a grounded neutral conductor which will also cause a trip.
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#175050 - 02/20/08 03:44 PM Re: arc -faults [Re: Tom]
Rewired Offline
Member
Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
"attic fan" as in "in attic, mounted ON the roof" or one of them "whole house fans"??
I didnt think an attic fan needed AFCI
Top
#175052 - 02/20/08 05:39 PM Re: arc -faults [Re: tomselectrc]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Unless the fan is actually located IN the bedroom ... I don't see where the requirement for the AFCI exists. The code is pretty clear ... every "outlet" ... and a switch is not an outlet.

In a like manner, simply having the fan pull air from the bedroom does not place it 'in' the room. I suppose a bath fan, where the fan is directly mounted to a hole in the ceiling, could be considered 'in' the bedroom. Let there be even a foot of duct, though, and it's not in the bedroom.

Otherwise, I agree that the fan is likely in need of replacement.
Top
#175053 - 02/20/08 06:04 PM Re: arc -faults [Re: renosteinke]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1309
Loc: Alaska
Put the fan on a different circuit that is not feeding the rooms
_________________________
"Live Awesome!" - Kevin Carosa
Top
#175054 - 02/21/08 04:38 AM Re: arc -faults [Re: sparkyinak]
tomselectrc Offline
Member
Registered: 03/14/04
Posts: 50
Loc: warren mi us
the fan is on it's own curcit,it is in the stairway that is in the bedroom. it is not in the attic.it is a 2 speed fan . check out all connection. next step is to see if breaker is bad.are there any exceptions to the arc-fault rule that i have missed?
Top
#175065 - 02/21/08 12:11 PM Re: arc -faults [Re: tomselectrc]
BPHgravity Offline
Member
Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
Exchanging the breaker to see if it is defective is a quick and easy way to eliminate that from the equation.

However, I agree with several of the above statements regarding the age of the equipment and it being the likely problem. 30 year old equipment will simply not be compatable with AFCI technology.

While it may not be practical or economically feasible to replace the entire fan assembly, you may be able to simply replace the motor and controller components.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter
Top
#175068 - 02/21/08 01:45 PM Re: arc -faults [Re: BPHgravity]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
Since this is an individual circuit it should be pretty easy to diagnose. At the panel (with the breaker off) check for continuity between the ground and neutral when disconnected from the bus. If it is anything but infinity that is probably the trouble (ground neutral short). Work your way back to the motor until you find it. Next step would be to temporarily hook it up to a regular breaker and hang your clamp on across the ground. It should stay zero. If you have something, I would suspect an intermittent grounded motor winding (real ground fault).
_________________________
Greg Fretwell
Top
#175092 - 02/22/08 05:37 AM Re: arc -faults [Re: gfretwell]
tomselectrc Offline
Member
Registered: 03/14/04
Posts: 50
Loc: warren mi us
thanks for the feedback i'm going to see if i can move the switch on the stairway landing hopefully he will except that instead of changeing the motor
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Admin), 117 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals