#174771 - 02/13/08 08:03 AM Lighting on 30 amp breaker??
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 826
Loc: Michigan
277 Lgts 6 tube T 5's or 6 tube &8's . Can you put them on a 30 amp breaker to get more on a Circuit using #10 wire to feed them?
Yoopers


210.21A says No looked it up thanks anyway


Edited by Yoopersup (02/13/08 08:10 AM)
Top
2017 / 2014 NEC & Related Books and Study Guides
#174774 - 02/13/08 08:45 AM Re: Lighting on 30 amp breaker?? [Re: Yoopersup]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1310
Loc: Alaska
according to the 2008 NEC, most sockets of flouresent fixtures are not rated for 750 watts there for they are not "heavy duty" If that is the case with your fixtures, then no you can not use a 30. If you are doing a one for one swap out of HIDs to Highbay Flouresent, More then likely you can use a 20 with no problem.
_________________________
"Live Awesome!" - Kevin Carosa
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:22 PM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 89 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals