#174676 - 02/11/08 09:42 AM avery weightronicsSilo level indicators
ricker Offline
Member
Registered: 11/30/07
Posts: 15
Loc: california
Hello, the aggregate plant I work at uses a great deal of siemens-milltronics control equipment for silo level indicators. They also use this brand for their belt scales. I recently replaced one of these belt scales with a Beltweigh system, which has worked flawlessly since its installation, whereas the siemens lasted about 3 days. Unfortunately, Beltweigh doesn't deal in level indicators, so I would like to know if anyone can recommend another brand of level indicator to replace the siemens. In addition to their products being unreliable, they offer very poor customer service. Thanks.
Top
Work Gear for Electricians and the Trades
#174678 - 02/11/08 01:22 PM Re: avery weightronicsSilo level indicators [Re: ricker]
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
We use pressure, level, temp, and pressure diff instruments from Rosemount


Trouble Free for the most part
Top
#174691 - 02/11/08 06:13 PM Re: avery weightronicsSilo level indicators [Re: ricker]
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
I used Rosemount for 20+ years with very few, if any problems at all.
Are you talking about solids? I also used Weightronix and Fairbanks load cell systems for weight-based measurements.


Edited by Redsy (02/11/08 06:17 PM)
Top
#174699 - 02/11/08 08:13 PM Re: avery weightronicsSilo level indicators [Re: Redsy]
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
My main problem with Milltronics has been that the Tefzel surface of the ST-H transducers delaminate from the filler. Energy gets eaten up in reflections on both Tx & Rx. The units I deal with have a parameter 83 which displays dB/uV. A delaminated surface will usually cause a level >60dB, to drop to the teens or 20s. You can press against the hard surface and feel a little give when this happens. I couldn't tell you the number of these that we have replaced at around $500/unit. Finally, I started scoring the surface along the outer edge and peeling off the Tefzel. The filler within has a little give to it but exhibits good dielectric resistance the piezo within is still protected.

You really need the programmer to deal with these units. The signal thresholds for short and long pulses can be changed as the transducer reaches end of life.

The only other problem I have had is a failure of a very small Belling-Lee (English) fuse on the main board. I could only find one US supplier in Florida and they had prohibitive minimum order quantities.

Joe
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 50 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals