The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Yesterday at 04:48 AM
Temporarily feeding a panel...
by Potseal
09/29/16 11:05 PM
Massive power outage South Australia
by Meadow
09/29/16 06:46 AM
short circuit??
by Meadow
09/29/16 06:43 AM
Norwegian power?
by Meadow
09/29/16 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 12
sparky 10
gfretwell 8
Potseal 7
sparky66wv 6
Who's Online
0 registered (), 285 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#174583 - 02/08/08 11:18 AM VFD Questions
oldsparky Offline
New Member

Registered: 02/08/08
Posts: 1
Loc: New England
I am having some VFD issues, looking for advice. Can the line and load conductors from a VFD be in the same raceway and can the loads from multiple VFD's be in the same raceway. I have reviewed multiple VFD manufacturers installation manuals with no good direction.

Top
2014 / 2011 NEC & Related Books and Study Guides
#174602 - 02/08/08 05:49 PM Re: VFD Questions [Re: oldsparky]
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
oldsparky,

I have installed several VFDs with the line & load conductors in the same raceway, and they worked fine for years.

I did however have a problem with voltages induced in a VFD with a 5 volt control circuit that shared a raceway with the load conductors. The VFD load conductors were inducing about 8 volts in the control wires and if I let go of the stop button during the ramp-to-stop period, the motor started up again.

For various reasons, we couldn't run a separate contol conduit, so we actually bought a new drive with a 10 volt control circuit and the problem went away.

That all being said, I would call your suppliers VFD man. He should be able to advise you.

BTW,

Are they Allen Bradley?


Edited by Redsy (02/08/08 05:56 PM)

Top
#174649 - 02/10/08 10:14 AM Re: VFD Questions [Re: Redsy]
JValdes Offline
Member

Registered: 06/03/07
Posts: 308
Loc: South Carolina
Seperate line and load conductors. Seperate signaling (control) circuits. Yes, individul conduits. Install a line reactor for each control (VFD). If motor is more than 100' away from drive install a load reactor. Inductive currents from the drive output will dirty up the input conductors causing nuisance tripping of the drive. The only place where the conductors should meet is in the control panel. Keeping control, line and load away from each other. You can use one breaker and a terminal block for several drives. But you should use seperate line reactors.

Note: Some VFD's have the reactor built in.
Try http://www.baldor.com and look under brochures or manuals. You can get anything you want there in PDF format.
Check http://www.transcoil.com. Or search Trans Coil Inc. for line and load reators and further information.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals