#174480 - 02/05/08 05:46 PM Bathroom exhaust fans
HCE727 Offline
Member
Registered: 11/11/05
Posts: 186
Loc: Delaware County, PA, USA
Do bathroom exhaust fans have to be switched with the lighting or can they be individually switched?
_________________________
Hank
Top
Work Gear for Electricians and the Trades
#174483 - 02/05/08 06:15 PM Re: Bathroom exhaust fans [Re: HCE727]
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Unless some local ordinance requires it, I can't think of any requirement to have them come on at the same time.

Top
#174496 - 02/06/08 03:38 AM Re: Bathroom exhaust fans [Re: Redsy]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
As a HO as well, I'd say it's preferable to have the fan on a separate switch. Switch with a timer is best.
Top
#174501 - 02/06/08 05:09 AM Re: Bathroom exhaust fans [Re: SteveFehr]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
HCE:
Design issue. Most commercial have fan on with lighting, and some local Health Depts require it, but I have no substantiation for that.

_________________________
John
Top
#174504 - 02/06/08 07:18 AM Re: Bathroom exhaust fans [Re: HotLine1]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Hotline,

Out here in CA all commercial and industrial occupancies require the fan to be switched with the lights.

Either that or the fan must run continuously, or be on a timer so that the fan is on during business hours.

Of course, I don't have a substantiation for it either laugh
Top
#174505 - 02/06/08 07:23 AM Re: Bathroom exhaust fans [Re: HotLine1]
togol Offline
Member
Registered: 09/15/05
Posts: 421
Loc: NW In. USA
I was wondering if anyone has ever considered using a humidistat for the fan in place of switches or timers .

it makes it hands-free and 120v units are available, could even remote a sensor and drive the fan with a relay and xfmr
_________________________
Tom
Top
#174510 - 02/06/08 08:43 AM Re: Bathroom exhaust fans [Re: togol]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
For residences, IRC 2006, M1507.3 requires a bathroom or toilet room to have "Mechanical exhaust capacity of 50cfm intermittent or 20cfm continuous." IRC sets no requirement for how this is implemented, only that the capacity must be there. Same switch, separate switch, humidistat, timer, etc- all OK by IRC.

Commercial is different. IMC 2006 400.3 requires commercial bathrooms in dorms, hotels, etc, to have 35cfm ventilation/person. (Continuous is implied.) As 0 people are in the bathroom when the lights are off and 0cfm required, the fan can be tied into the light switch. I'm not familiar enough with IMC to know any other subtleties of the code, or what specifically applies to restrooms in stores or offices.
Top
#174513 - 02/06/08 09:12 AM Re: Bathroom exhaust fans [Re: SteveFehr]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
I always seperate fan and light, unless HO wants both together. No violation of NEC in residential.
I used spring timers when my daughters (4) were still at home. Now, we just use regular swiches so we do not have to listen to the fan until it times out.
Top
#174525 - 02/06/08 04:26 PM Re: Bathroom exhaust fans [Re: JValdes]
JoeyD Offline
Member
Registered: 01/19/08
Posts: 21
Loc: Arlington MA
I was told in MA the building code states the fan has to come on with the light if there is no windows in the bathroom.
I seperate then unless the owner wants them on at the same time. In a half bath I like the fan on with the lights and using panasonic you can't hear them anyways
Top
#174527 - 02/06/08 05:51 PM Re: Bathroom exhaust fans [Re: JoeyD]
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6778
Loc: Brick, NJ USA
Electure:
Yes, I agree. Comm is on w/lights, or TC control for occupied hrs. I can't place a Article thou, and say it's a design thing.
_________________________
John
Top

Member Spotlight
Member Since: 05/03/03
Posts: 1137
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals