The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
1 registered (gfretwell), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#174420 - 02/04/08 12:35 PM Lights dimming?
petey_c Offline
Member

Registered: 01/30/05
Posts: 62
Loc: Miller Place, NY USA
Here's a question that's probably already been asked. Occasionally when I'm working residential, a customer will ask, "Why do the lights dim momentarily when my A/C (or other heavy load device) turns on. I try and give a non-technical or tech-light explanation. It's usually the "electricity is like water in a plumbing line. You're taking a shower and someone flushes the toilet. You experience a momentary loss of "pressure."" Any thoughts? pete

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#174427 - 02/04/08 04:31 PM Re: Lights dimming? [Re: petey_c]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1295
Loc: Alaska
It can be several things. It is all dependent on the problem.

* Too many things on the circuit and it is trying to trip the breaker but the surge is over before it can. in layman's term: It is like trying to stick 10 pounds of crap in a 5 pound box.

* The service capacity is too much at the transformer and can not carry the load. In layman's term: It is like the little engine that coundn't.

*They have a serious problem with their service neutral. There is potential fire or electrical damage to equipment due to higher the normal voltage. In layman's term:
it is like there is potential fire or electrical damage to equipment due to higher the normal voltage.
_________________________
"Live Awesome!" - Kevin Carosa

Top
#174435 - 02/04/08 05:55 PM Re: Lights dimming? [Re: sparkyinak]
JoeTestingEngr Offline
Member

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
Just explain to them how a motor takes much more current to start and get up to speed than to run at that speed. Have them think about how little fuel is required to hold 60MPH on the highway. It will be intuitive to them that it takes more when they go from zero to sixty. Then have them consider what it would take from under their hood if their car could even come close to zero to sixty in under three seconds. Then just explain that the huge current draw causes a voltage drop that causes the lights to dim even though they draw little current.
Joe

Top
#174445 - 02/05/08 03:45 AM Re: Lights dimming? [Re: JoeTestingEngr]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Just tell them the truth- the power company are a bunch of cheapasses and undersize the aerial drop from the powerline transformer to their house, and then when big motors like a heat pump start up, they draw more power than the rest of the house combined for a fraction of a second. So when the big motor on heat pump starts up, the in-rush of current drops the voltage on the line into the house a few volts. It takes surprisingly little voltage drop to make a notible dimming of lights.

You can even point out that a typical 5hp motor has inrush of 168A, even if it only draws 20A while it's running. Shoot, if the pole pig is only 25kVA, that in-rush would completely saturate the transformer and dim *everyone's* lights.

Top
#174448 - 02/05/08 04:01 AM Re: Lights dimming? [Re: SteveFehr]
petey_c Offline
Member

Registered: 01/30/05
Posts: 62
Loc: Miller Place, NY USA
Steve, Yeah, the PoCos are cheapasses... I've seen people's eyes start to glaze over when I start anything remotely technical (tech-lite). They seem to relate better to the sudden inrush of hot/cold water whilst they're taking a shower, than current. Had the pleasure of spending several months as a guest of the Navy out in Chesapeake at the Residence Inn off of Greenbriar. Nice area, considered getting my Va/NC license ('cause I was bored), but couldn't get the paperwork sent to me. Wife wouldn't be able to find it. Thanks for all the replies

Top
#174626 - 02/09/08 07:06 PM Re: Lights dimming? [Re: petey_c]
harold endean Offline
Member

Registered: 02/16/02
Posts: 2248
Loc: Boonton, NJ
Another thought, Ask the homeowner (HO) if the dimming lights are in just one room or in the whole house. Sometimes the problem is in the branch circuit. If the lights dim in the whole house the problem could be in the main service panel, the meter, the connections at the head or out on the street. It might take some time and patience to figure out just where the problem is located.

Top
#174645 - 02/10/08 08:17 AM Re: Lights dimming? [Re: harold endean]
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
If they are having a problem with the lights flickering when an A/C starts, assuming there is no actual problem with the wiring or the service etc, you might want to try putting a " kick start" hard starting device in the A/C unit. I did on my parent's A/C (for other reasons) and now there is little or no flicker in their lights.

A.D

Top
#174693 - 02/11/08 06:27 PM Re: Lights dimming? [Re: Rewired]
wire_twister Offline
Member

Registered: 07/25/07
Posts: 265
Loc: Georgia USA
Do you have a link for the "Kick start" device, I might want one for my house. 15kva pole pig + 5 ton heat pump = dim lights for split second.
_________________________
Jimmy

Life is tough, Life is tougher when you are stupid

Top
#174708 - 02/12/08 03:42 AM Re: Lights dimming? [Re: wire_twister]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
http://www.kickstartoem.com/

It's a capacitor and a relay wired in parallel with the motor. Don't most condensors come with one of these already built into it?

Top
#174710 - 02/12/08 06:05 AM Re: Lights dimming? [Re: wire_twister]
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
They are also known as hard start kits. Talk to your AC&R technician to verify that there is not another reason for the large current draw when starting.