The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 8
Trumpy 6
Who's Online
0 registered (), 261 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#174381 - 02/03/08 11:59 AM Proper use of ground bushings?
SP4RX Offline
Member

Registered: 10/01/07
Posts: 56
Loc: Edmonton, Alberta, Canada...eh
Hi all, I have a question for you about when and why a person would use a ground bushing...it has never really been explained to me.

One guy I worked with wanted one at either end of a run of Teck cable, but he couldn't explain the reasoning for this. The other day I was talking with another co-worker about this and he says it isn't necessary.

Back when I was doing residential work it was necessary to use a ground bushing on the connector inside the panel to properly bond the service entrance conduit. I guess the connector doesn't provide adequate bonding in this situation?

The code wording doesn't make sense to me so I figured you might be able to explain it a lil' better.


Thanks a bunch

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#174385 - 02/03/08 12:52 PM Re: Proper use of ground bushings? [Re: SP4RX]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1296
Loc: Alaska
Bonding bushing should be used anytime a metal conduit enters any type of enclosure when the conductivity can not be ensured across where the conduit and enclosure meet. One example is a cocked conduit or a conduit is not square to the enclosure. this will prevent the locknut(s) from mating squarely to the box. Another example is the concentric / eccentric knockouts. Although they are usually rated for carry fault current, some times they limited on the rating or the concentric / eccentric sometimes get banged around during installation. When in doubt, throw on a bonding bushing.
_________________________
"Live Awesome!" - Kevin Carosa

Top
#174392 - 02/03/08 04:47 PM Re: Proper use of ground bushings? [Re: sparkyinak]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Service conduits require bond bushings because you simply can't count on the lock nuts to handle fault current of service conductors. There was a picture floating around IAEI a while ago of a 4" conduit that had burned out the whole area of the enclosure where the lock nuts were.
_________________________
Greg Fretwell

Top
#174393 - 02/03/08 05:11 PM Re: Proper use of ground bushings? [Re: gfretwell]
Sixer Offline
Member

Registered: 08/08/05
Posts: 264
Loc: Canada
Sparkyinak and gfretwell nailed it on the head.
I'll elaborate a bit further:
The reasoning for requiring a bonding bushing on a service entrance is that locknuts need to bite through paint or rust in order to contact bare metal and give good continuity to ground. Since we're talking about service entrances there's a high fault current available. Should a conductor short against the connector or conduit you want this to have good ground continuity.

Another example of requiring a bonding bushing or ground wedge would be when using PVC boxes and having teck cable or metal conduit run between them. The conduit or the armour of the cable would not be grounded by just using locknuts against a PVC box.
_________________________
Sixer

"Will it be cheaper if I drill the holes for you?"

Top
#174423 - 02/04/08 01:14 PM Re: Proper use of ground bushings? [Re: Sixer]
GA76JW Offline
Member

Registered: 03/20/04
Posts: 195
Loc: Suwanee, GA USA
We also use bonding bushings when we have a run of flex in between two points. Most usually with transformer feeds on the primary and secondary sides.
_________________________
"If common sense was common, everyone would have it"-not sure, someone here


Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals