The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 259 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#174261 - 01/30/08 03:24 PM Size of Equipment Grounding Conductors.
Sparkman Offline
New Member

Registered: 01/17/08
Posts: 1
Loc: North Carolina
Can anyone shed any light on 250.122(B)? Thank you in advance.

2014 / 2011 NEC & Related Books and Study Guides
#174265 - 01/30/08 04:25 PM Re: Size of Equipment Grounding Conductors. [Re: Sparkman]
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Sure, what do you want to know?
Bob Badger
Construction & Maintenance Electrician

#174283 - 01/30/08 10:48 PM Re: Size of Equipment Grounding Conductors. [Re: iwire]
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
Short answer. If you upsize the conductors for something like voltage drop you also have to upsize the EGC.
Greg Fretwell

#174284 - 01/31/08 03:34 AM Re: Size of Equipment Grounding Conductors. [Re: gfretwell]
SteveFehr Offline

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
They want to you increase the EGC by the same ratio you increase the current conductors. These #s are availible in Table 8

For example, lets say you have a 125A circuit (Normally #2 Cu w/#8 EGC) but have to increase the conductors to 1/0 to allow for derating:

#2 = 66kcmil
1/0 = 106kcmil
Increase is 60%.

#8 = 16.5kcmil.
16.5kcmil * 160% = 26.4kcmil

Looking through the table, #6 = 26.2kcmil, and would be the proper ground wire to use.

#174294 - 01/31/08 01:15 PM Re: Size of Equipment Grounding Conductors. [Re: SteveFehr]
resqcapt19 Offline

Registered: 11/10/00
Posts: 2209
Loc: IL
The interesting part is where you have a circuit protected at 30 amps or less....the EGC must be the same size as the circuit conductors. This often comes into play for parking lot lighting where you may be using a #4 or 6 on a 20 amp circuit.

#175836 - 03/12/08 11:09 AM Re: Size of Equipment Grounding Conductors. [Re: Sparkman]
kohli Offline
New Member

Registered: 03/10/08
Posts: 9
Loc: Ohlo Putnam Co
This is like many parts of the NEC which has been around from the early nightteen 30s when large pipe organ was popular

Now we have keyboardsand large amp systems or sound systems which make some of the old way of doing things of date , remember knob and tube, worked well in its day

Just food for thought thank you

#175838 - 03/12/08 11:54 AM Re: Size of Equipment Grounding Conductors. [Re: kohli]
BPHgravity Offline

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
The conflict described by Don also occurs on equipment such as motors and air conditioning equipment that may have conductors that are permitted to be sized smaller than the branch circuit overcurrent device.

In many cases, the contractor will install conductors sized based on the max overcurrent device instead of the minimum branch circuit size and NOT increase the EGC in proportion.

The contractor doesn't understand why the EGC has to be increase when a smaller EGC is normally permitted for that circuit rating.

There were a couple proposals submitted this past code cycle that tried to clear up this issue, but none were accepted.

I have tried to come up with a good rewrite of 250.122(B) myself without much luck.