The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
01/18/17 12:03 AM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 20
HotLine1 19
gfretwell 13
ghost307 12
Trumpy 12
Who's Online
1 registered (Webmaster), 0 Guests and 73 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#174261 - 01/30/08 03:24 PM Size of Equipment Grounding Conductors.
Sparkman Offline
New Member

Registered: 01/17/08
Posts: 1
Loc: North Carolina
Can anyone shed any light on 250.122(B)? Thank you in advance.

Top
2017 / 2014 NEC & Related Books and Study Guides
#174265 - 01/30/08 04:25 PM Re: Size of Equipment Grounding Conductors. [Re: Sparkman]
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Sure, what do you want to know?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#174283 - 01/30/08 10:48 PM Re: Size of Equipment Grounding Conductors. [Re: iwire]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9062
Loc: Estero,Fl,usa
Short answer. If you upsize the conductors for something like voltage drop you also have to upsize the EGC.
_________________________
Greg Fretwell

Top
#174284 - 01/31/08 03:34 AM Re: Size of Equipment Grounding Conductors. [Re: gfretwell]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
They want to you increase the EGC by the same ratio you increase the current conductors. These #s are availible in Table 8

For example, lets say you have a 125A circuit (Normally #2 Cu w/#8 EGC) but have to increase the conductors to 1/0 to allow for derating:

#2 = 66kcmil
1/0 = 106kcmil
Increase is 60%.

#8 = 16.5kcmil.
16.5kcmil * 160% = 26.4kcmil

Looking through the table, #6 = 26.2kcmil, and would be the proper ground wire to use.

Top
#174294 - 01/31/08 01:15 PM Re: Size of Equipment Grounding Conductors. [Re: SteveFehr]
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The interesting part is where you have a circuit protected at 30 amps or less....the EGC must be the same size as the circuit conductors. This often comes into play for parking lot lighting where you may be using a #4 or 6 on a 20 amp circuit.
Don
_________________________
Don(resqcapt19)

Top
#175836 - 03/12/08 11:09 AM Re: Size of Equipment Grounding Conductors. [Re: Sparkman]
kohli Offline
New Member

Registered: 03/10/08
Posts: 9
Loc: Ohlo Putnam Co
This is like many parts of the NEC which has been around from the early nightteen 30s when large pipe organ was popular

Now we have keyboardsand large amp systems or sound systems which make some of the old way of doing things of date , remember knob and tube, worked well in its day

Just food for thought thank you

Top
#175838 - 03/12/08 11:54 AM Re: Size of Equipment Grounding Conductors. [Re: kohli]
BPHgravity Offline
Member

Registered: 04/08/03
Posts: 141
Loc: Port Charlotte, Florida
The conflict described by Don also occurs on equipment such as motors and air conditioning equipment that may have conductors that are permitted to be sized smaller than the branch circuit overcurrent device.

In many cases, the contractor will install conductors sized based on the max overcurrent device instead of the minimum branch circuit size and NOT increase the EGC in proportion.

The contractor doesn't understand why the EGC has to be increase when a smaller EGC is normally permitted for that circuit rating.

There were a couple proposals submitted this past code cycle that tried to clear up this issue, but none were accepted.

I have tried to come up with a good rewrite of 250.122(B) myself without much luck.
_________________________
Bryan P. Holland, ECO.
Secretary - IAEI Florida Chapter

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals