The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
breaker meltdown
by crselectric
09/24/16 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 9
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 267 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#174042 - 01/25/08 01:22 PM Is This Reasonable ?
wendel Offline
Member

Registered: 08/07/04
Posts: 57
I am adding two new bedrooms each with a bathroom. There will be 10@5" can lights (5 each bedroom and bath) plus the usual receptacles. No AC or other high load appliances.

I was told by an electricial that I needed a 50 amp subpanel for the the bedroom circuits which seems excessive. Is this reasonable?

What does the NEC require for bedrooms with bathrooms?

Thank you for your help.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#174050 - 01/25/08 03:32 PM Re: Is This Reasonable ? [Re: wendel]
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
A 50 amp panel sounds reasonable to me. They're dirt cheap. Why does it seem excessive to you?

Top
#174052 - 01/25/08 03:43 PM Re: Is This Reasonable ? [Re: SolarPowered]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
Something makes me feel that AFCI's may be required on this installation as well.

Just my thought from an "out of towner".
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#174053 - 01/25/08 04:02 PM Re: Is This Reasonable ? [Re: Trumpy]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
Wendel:
May be a cost effective way to do job; materials and/or labor. Depends on the length of the HR's and the work to get from point A to point B.

You neglected to list the wattage of the recess; also are exhaust fans or fan/lights in the 2 baths?

Sounds OK.

As to AFCI's....unless you are in a state like NJ that amended the NEC...you need them
_________________________
John

Top
#174087 - 01/26/08 06:53 AM Re: Is This Reasonable ? [Re: HotLine1]
wendel Offline
Member

Registered: 08/07/04
Posts: 57
Thank you all for your help.

I guess my real question is how do you determine the needed number of circuits for a given number of electrical devices?

I have two new bedrooms to feed from the subpanel. Each BR will have 5 recessed lights @60 watts, a ceiling fan, a bathroom fan and 6 wall receptacles.

I have an existing 40 amp circuit at the main panel that I want to use. The wire is inplace and was used previously for a cooktop (we're now gas).

The goal is to save cutting into the wall at the main breaker box to run another wire (the electrician said he would need to cut). I am trying to determine if a 240v, 40 amp circuit to the subpannel that will be used for the 2 BRs will be acceptable to NEC provisions.

Thanks again for your insight.

Top
#174089 - 01/26/08 07:47 AM Re: Is This Reasonable ? [Re: wendel]
LK Offline

Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
Just from what I have read, the total area in sq feet that you have added to the home, has increased, I may be that your or original electrical was under sized or had out grown todays needs, just a guess, the sub panel that is there is most likely wired wrong, my bet is it does not have a isolated neutral, or you do not have eniough spaces in the old panel, this could be the reason, the electrician needs to open the wall, also I did not see anything about inter connected smokes, and remember another circuit for the bathroom GFCI.

Top
#174091 - 01/26/08 08:28 AM Re: Is This Reasonable ? [Re: LK]
wendel Offline
Member

Registered: 08/07/04
Posts: 57
Thank you, LK. Let me clarify.

The existing wiring is more than adequate. The house is only 10 years old. The purpose of the subpanel was more to save money running the needed wire back to the main panel since copper is so expensive.

The subpanel will have an 8/3 feed that already exists (no new load). From what I have read it seems the total load calculation can be approximated by ~3 watts (VA) per square foot of new area. Since these are bedrooms, there are no big appliance/motor loads.

In doing the NEC method it seems all I need is ~11 amps@240 volts. I agree I may need many individual circuits (smoke, GFI etc) but the total load this subpanel would need to supply would be significantly less than 40 amps@240 volts I have available... correct?.

Here's the calculation:

General Light and Receptacle Load
600 (2@300)sqft x 3VA = 1800VA

Total General Load Less Demand
sum of above less T220.11 demand
sum of above = 1800VA
first 3000 at 100 % = 3000
next 117,000 at 35% = -420
remainder at 25% = 0
sum less demand = 2580VA

Computed Amperage
2580 divided by 240 = 11Amps

Top
#174122 - 01/27/08 04:04 AM Re: Is This Reasonable ? [Re: wendel]
petey_c Offline
Member

Registered: 01/30/05
Posts: 62
Loc: Miller Place, NY USA
Here you'd need 1 separate 20 A ckt for each bath. Some towns on Long Island require you to also have a separate ckt for an A/C in each bedroom, in addition to the regular outlet circuit (AFCI protected of course). So, the sub-panel doesn't really seem out of line.
As a side-note; A fellow sparky who has been working at Home Depot to supplement his income, related this story to me. Seems down the road from his house, a HO wanted to have some high hats installed and contacted an unlicensed "pro." As he's removing some cans from his truck, SCPD pulls in the driveway behind him. When he was asked what he was doing, he replied, "Just doing some electrical work." "Do you have a license?" "Ummm no." The officer was nice enough to provide him with some nice bracelets and a trip to the newly refurbished station house.

Top
#174136 - 01/27/08 08:27 AM Re: Is This Reasonable ? [Re: petey_c]
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6785
Loc: Brick, NJ USA
"As he's removing some cans from his truck, SCPD pulls in the driveway behind him. When he was asked what he was doing, he replied, "Just doing some electrical work." "Do you have a license?" "Ummm no." The officer was nice enough to provide him with some nice bracelets and a trip to the newly refurbished station house."

Interesting...wheels of justice in Suffolk Cty are really rolling along! What was the charge??

Here in NJ...a formal written complaint has to be filed with the Board of Examiners. Usually, by the time the paperwork is processed, the "pro" is long gone!

LK.....any thoughts on this comment???
_________________________
John

Top
#174139 - 01/27/08 09:42 AM Re: Is This Reasonable ? [Re: HotLine1]
wendel Offline
Member

Registered: 08/07/04
Posts: 57
Thanks, petey_c for your insight.

So since there's no AC in the bedroom (it's central AC for the house) I will need a 20 amp (bathroom) and 15 amp(lights and receptacles) circuit for each bedroom. So the total for the two bedrooms will be 4 new circuits, if I understand you correctly. A 40 amp feed to a 100 amp subpanel box seems to be more than adequate.

Top