#173992 - 01/24/08 05:54 PM Portable generator
jem Offline
New Member
Registered: 04/30/07
Posts: 8
Loc: nc
Customer wants to use a portable generator to power some house circuits. This generator has bonded nuetral/ ground. Since generator is bonded, must I use a transfer switch that switches the nuetral and can the existing ground rod be used for grounding the generator.
Top
2017 / 2014 NEC & Related Books and Study Guides
#173995 - 01/24/08 06:09 PM Re: Portable generator [Re: jem]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Yes, switch the neutral.

No, you don't tie s portable generator to the ground rod.

If he's mounting the generator permanently, it's no longer a portable generator.

My advice? If you're using a portable genny, use extension cords, and portable lights too. Don't even try to tie it in. If you want a stand-by genny, get a real one, and install it properly.
Top
#173996 - 01/24/08 06:10 PM Re: Portable generator [Re: jem]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1309
Loc: Alaska
You should always use a transfer switch. And yes on the ground rod
_________________________
"Live Awesome!" - Kevin Carosa
Top
#173998 - 01/24/08 06:28 PM Re: Portable generator [Re: renosteinke]
32VAC Offline
Member
Registered: 06/28/04
Posts: 203
Loc: Alice Springs, NT, Australia
Originally Posted By renosteinke


My advice? If you're using a portable genny, use extension cords, and portable lights too. Don't even try to tie it in. If you want a stand-by genny, get a real one, and install it properly.


Agreed. For the generator at home, the extension cords live in a box all marked with where they run to (fridge 1, fridge 2, freezer and lights).

The lights are also in the box (2x 240VAC trouble lights with rough service 250-260V globes fitted). The generator has four outlets fitted for the four main leads with a double adaptor on the end of the lighting lead.

Piece of pie when needed, no hunting around for leads when you need them.
Top
#174014 - 01/25/08 12:42 AM Re: Portable generator [Re: sparkyinak]
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8560
Loc: SI,New Zealand
Originally Posted By sparkyinak
You should always use a transfer switch. And yes on the ground rod


You never tie a portable generator to a grounding system associated with a house, otherwise you may get circulating earth currents, at the least you may get noise on you radio, at the worst you could kill someone.

A generator is a seperately derived system, it should always be kept away from the mains wiring, unless it is fed in through a transfer switch.

I have to go with what Darren and John are saying, if you only need power when the mains fails and you don't need it instantly, I would go for the labelled flexes and lights, etc.
After all, you can't run a whole house on most "portable" generators anyway.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#174016 - 01/25/08 02:06 AM Re: Portable generator [Re: Trumpy]
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Originally Posted By Trumpy
You never tie a portable generator to a grounding system associated with a house, otherwise you may get circulating earth currents, at the least you may get noise on you radio, at the worst you could kill someone.


Mike, under the NEC that really depends on the installation.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#174020 - 01/25/08 07:16 AM Re: Portable generator [Re: iwire]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I think the key word here is "portable."

Some folks think that they are somehow improving things if they bang a ground rod whenever they use a portable, or vehicle mounted, generator. I think we've established that doing so accomplishes nothing ... as the ground rod is essentially irrelevant to clearing faults.

That everything in the building needs to be bonded, and that these paths need to go back to the generator, is another subject. That's why I say "switch the neutral;" there's no way for the electricity to go anywhere else.

Naturally, I assume that the extension cords have intact three-prong plugs!

I don't think I have ever run a wire from a genny, directly to a ground rod. Rather, the transfer switch provided the point where the generator ground was tied into the building's ground system. With a portable genny, this is accomplished by that third prong on the plug.
Top
#174021 - 01/25/08 07:44 AM Re: Portable generator [Re: renosteinke]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I am not sure why they would even bond a truly portable generator. What is the point? A single frame to neutral fault is exactly what you are doing with the bond and two phases faulted to the frame would operate the OC device anyway (HOPEFULLY)
neither is actually a "grounded" conductor. It is arbitrary which one you bond.
_________________________
Greg Fretwell
Top
#174026 - 01/25/08 10:15 AM Re: Portable generator [Re: gfretwell]
jem Offline
New Member
Registered: 04/30/07
Posts: 8
Loc: nc
I see portable generators cord connected via a 4 wire cord to a power inlet on a generator panel fairly frequently. What I would like to know is if the portable generator is bonded (internal to the unit) and the neutral is switched at the transfer switch (seperately derived system) a grounding electrode is required. Can a tap be run from the service GEC to accomplish this. If the neutral is not switched (not a seperately derived system), you have a bond at the generator on the load side of the service disconnect when the generator is plugged in.
Top
#174142 - 01/27/08 11:41 AM Re: Portable generator [Re: jem]
Rewired Offline
Member
Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
If the generator has the neutral bonded to "ground" in the generator and a switched neutral is employed in the transfer switch ( as it should be with a bonded generator neutral), a ground electrode should not be used or needed because the neutral is still bonded to ground through the generator.. Doing anything else may cause circulating currents in the grounding / bonding conductors and will defeat the purpose of the switched neutral in the transfer switch.

A.D
Top
Page 1 of 2 1 2 >

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
Today at 02:08 AM
License exam
by TRUE POWER
Yesterday at 09:16 PM
Looking for older post
by sparkyinak
Yesterday at 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
0 registered (), 79 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 11/11/05
Posts: 190

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals