The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Temporarily feeding a panel...
by HotLine1
Today at 07:07 PM
Locked rotor, no burnout
by jraef
Today at 01:18 PM
Massive power outage South Australia
by Meadow
Today at 06:46 AM
short circuit??
by Meadow
Today at 06:43 AM
Norwegian power?
by Meadow
Today at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
sparky66wv 8
gfretwell 8
Vlado 6
Who's Online
0 registered (), 296 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#173992 - 01/24/08 05:54 PM Portable generator
jem Offline
New Member

Registered: 04/30/07
Posts: 8
Loc: nc
Customer wants to use a portable generator to power some house circuits. This generator has bonded nuetral/ ground. Since generator is bonded, must I use a transfer switch that switches the nuetral and can the existing ground rod be used for grounding the generator.

Top
2014 / 2011 NEC & Related Books and Study Guides
#173995 - 01/24/08 06:09 PM Re: Portable generator [Re: jem]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5300
Loc: Blue Collar Country
Yes, switch the neutral.

No, you don't tie s portable generator to the ground rod.

If he's mounting the generator permanently, it's no longer a portable generator.

My advice? If you're using a portable genny, use extension cords, and portable lights too. Don't even try to tie it in. If you want a stand-by genny, get a real one, and install it properly.

Top
#173996 - 01/24/08 06:10 PM Re: Portable generator [Re: jem]
sparkyinak Offline
Member

Registered: 07/08/07
Posts: 1286
Loc: Alaska
You should always use a transfer switch. And yes on the ground rod
_________________________
"Live Awesome!" - Kevin Carosa

Top
#173998 - 01/24/08 06:28 PM Re: Portable generator [Re: renosteinke]
32VAC Offline
Member

Registered: 06/28/04
Posts: 203
Loc: Alice Springs, NT, Australia
 Originally Posted By: renosteinke


My advice? If you're using a portable genny, use extension cords, and portable lights too. Don't even try to tie it in. If you want a stand-by genny, get a real one, and install it properly.


Agreed. For the generator at home, the extension cords live in a box all marked with where they run to (fridge 1, fridge 2, freezer and lights).

The lights are also in the box (2x 240VAC trouble lights with rough service 250-260V globes fitted). The generator has four outlets fitted for the four main leads with a double adaptor on the end of the lighting lead.

Piece of pie when needed, no hunting around for leads when you need them.

Top
#174014 - 01/25/08 12:42 AM Re: Portable generator [Re: sparkyinak]
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8530
Loc: SI,New Zealand
 Originally Posted By: sparkyinak
You should always use a transfer switch. And yes on the ground rod


You never tie a portable generator to a grounding system associated with a house, otherwise you may get circulating earth currents, at the least you may get noise on you radio, at the worst you could kill someone.

A generator is a seperately derived system, it should always be kept away from the mains wiring, unless it is fed in through a transfer switch.

I have to go with what Darren and John are saying, if you only need power when the mains fails and you don't need it instantly, I would go for the labelled flexes and lights, etc.
After all, you can't run a whole house on most "portable" generators anyway.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#174016 - 01/25/08 02:06 AM Re: Portable generator [Re: Trumpy]
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Originally Posted By: Trumpy
You never tie a portable generator to a grounding system associated with a house, otherwise you may get circulating earth currents, at the least you may get noise on you radio, at the worst you could kill someone.


Mike, under the NEC that really depends on the installation.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#174020 - 01/25/08 07:16 AM Re: Portable generator [Re: iwire]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5300
Loc: Blue Collar Country
I think the key word here is "portable."

Some folks think that they are somehow improving things if they bang a ground rod whenever they use a portable, or vehicle mounted, generator. I think we've established that doing so accomplishes nothing ... as the ground rod is essentially irrelevant to clearing faults.

That everything in the building needs to be bonded, and that these paths need to go back to the generator, is another subject. That's why I say "switch the neutral;" there's no way for the electricity to go anywhere else.

Naturally, I assume that the extension cords have intact three-prong plugs!

I don't think I have ever run a wire from a genny, directly to a ground rod. Rather, the transfer switch provided the point where the generator ground was tied into the building's ground system. With a portable genny, this is accomplished by that third prong on the plug.

Top
#174021 - 01/25/08 07:44 AM Re: Portable generator [Re: renosteinke]
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9012
Loc: Estero,Fl,usa
I am not sure why they would even bond a truly portable generator. What is the point? A single frame to neutral fault is exactly what you are doing with the bond and two phases faulted to the frame would operate the OC device anyway (HOPEFULLY)
neither is actually a "grounded" conductor. It is arbitrary which one you bond.
_________________________
Greg Fretwell

Top
#174026 - 01/25/08 10:15 AM Re: Portable generator [Re: gfretwell]
jem Offline
New Member

Registered: 04/30/07
Posts: 8
Loc: nc
I see portable generators cord connected via a 4 wire cord to a power inlet on a generator panel fairly frequently. What I would like to know is if the portable generator is bonded (internal to the unit) and the neutral is switched at the transfer switch (seperately derived system) a grounding electrode is required. Can a tap be run from the service GEC to accomplish this. If the neutral is not switched (not a seperately derived system), you have a bond at the generator on the load side of the service disconnect when the generator is plugged in.

Top
#174142 - 01/27/08 11:41 AM Re: Portable generator [Re: jem]
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
If the generator has the neutral bonded to "ground" in the generator and a switched neutral is employed in the transfer switch ( as it should be with a bonded generator neutral), a ground electrode should not be used or needed because the neutral is still bonded to ground through the generator.. Doing anything else may cause circulating currents in the grounding / bonding conductors and will defeat the purpose of the switched neutral in the transfer switch.

A.D