The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by LongRunner
01/16/17 07:42 AM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
gfretwell 11
sparkyinak 10
ghost307 10
Webmaster 8
Who's Online
2 registered (brsele, ghost307), 313 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#173953 - 01/23/08 12:17 PM GEC size at second building?
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9058
Loc: Estero,Fl,usa
If you are installing a GEC at a second building on a service do you still size to 250.66 on the service conductors or do you base it on the feeder?
_________________________
Greg Fretwell

Top
2014 / 2011 NEC & Related Books and Study Guides
#173954 - 01/23/08 01:00 PM Re: GEC size at second building? [Re: gfretwell]
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The size of the feeder to the building in question.

Check out 250.32(E) 2005
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#173964 - 01/23/08 08:39 PM Re: GEC size at second building? [Re: iwire]
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9058
Loc: Estero,Fl,usa
OK I was just concerned about what a "supply conductor" really meant. I assumed it was the feeder but I wanted to hear it ... as a sanity check. Thanks
_________________________
Greg Fretwell

Top
#173967 - 01/24/08 01:44 AM Re: GEC size at second building? [Re: gfretwell]
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I agree it could be clearer.......