#173829 - 01/19/08 05:40 PM Electric Heat change for 2008?
zapped208 Offline
Member
Registered: 02/18/03
Posts: 196
Loc: Somewhere in USA
My friend, who I work with on weekends, plus all my other work,had a plan review with our local inspector this past week.
He,I, will be wiring a new addition to a gated community, community building, with M/C cable.
Plans call for electric baseboard heaters, but inspector says we can not put 3750 watts of heat on a #12-20A circuit anymore, in a commerial area, only 3000 watts max on 20A & 5000 watts max for a 30A circuit.
Is this true?
_________________________
Shoot first, apologize later.....maybe
Top
2017 / 2014 NEC & Related Books and Study Guides
#173831 - 01/19/08 08:12 PM Re: Electric Heat change for 2008? [Re: zapped208]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
I think I would politely ask the inspector how he came up with those numbers.
Unless he’s applying some derating or other correction factors, I just can’t figure it.
The only NEC 2008 change for fixed electric space heating equipment is 424.19, regarding disconnecting means being rated for 125% of the total load.
Again, this requirement is for the total load, not the branch circuit rating.
He may be taking the 3750-Watt heater load and dividing it by 125% to get his 3000-Watt limit. If so, that’s not the correct way to do it.
The branch circuits are considered continuous loads, so can only be loaded to 80%. Such as 20A X 240V X 80% = 3840W or 3328W if it’s 208V.
That would be a 16A load. 16A X 125% = 20A rated disconnecting means. Most DPST line-voltage thermostats have a 22 Amp load rating, so the 125% requirement for the disconnecting means is already met.
Other than that, I’m at a loss to explain.



Top
#173835 - 01/20/08 05:40 AM Re: Electric Heat change for 2008? [Re: KJay]
zapped208 Offline
Member
Registered: 02/18/03
Posts: 196
Loc: Somewhere in USA
We thougth it did not make sense either.
Your allowed to do it resi, but not commerial?
I will challenge the inspector,cuz I usually win anyway.
_________________________
Shoot first, apologize later.....maybe
Top
#173863 - 01/21/08 09:30 AM Re: Electric Heat change for 2008? [Re: zapped208]
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
The Canadian Electrical code would allow #12 feeding base board heater to be loaded to the full 20 amps or 4800 watts on a 25 amp or 30 amp breaker depending on the availability from a manufacturer for a 25 amp breaker. #14 can be loaded to 3600 watts on a 20 amp breaker.
This is one of the very few places where a wire can be loaded to its full rating and only applies to baseboard heaters.
I know this is an NEC question except that unification of our respective codes is supposed to be a mutual objective.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 44 Guests and 20 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals