#173705 - 01/16/08 06:20 PM Botl in or stab in?  
rj  Offline
Member
Joined: Jan 2003
Posts: 21
Skidmore, Missouri, USA
I am in need of some information about bolt in breakers compared to stabe ins. I know that you are suppost to have a better connection with a bolt in, but what about maintenace in the long run. Myself I would rahter work and maintain the stabe in. Any others with that feeling or that bolt in is the best way to go?
Thanks for any input on this.


Work Gear for Electricians and the Trades

#173706 - 01/16/08 06:27 PM Re: Botl in or stab in? [Re: rj]  
wire_twister  Offline
Member
Joined: Jul 2007
Posts: 265
Georgia USA
I like the bolt in for areas with high load or vibration. I worked in manufacturing plants for about 16 years, most of the equipment was either Westinghouse or Square D bolt in type, all of it gave vary little trouble. As far as maint. goes we would shut down the panels once every other year and check the screws for tightness, I do not remember ever tightning one more than about 1/16 of a turn, of course all this was wired with copper wire, as it should be in an industrial setting.


Jimmy

Life is tough, Life is tougher when you are stupid

#173708 - 01/16/08 09:58 PM Re: Botl in or stab in? [Re: wire_twister]  
leland  Offline
Member
Joined: Aug 2007
Posts: 853
Lowell area, Ma. USA
Industrial: bolt in every time. reliability.

Resi: stab ins are fine, very low demand.


#173725 - 01/17/08 07:59 AM Re: Botl in or stab in? [Re: leland]  
SteveFehr  Offline
Member
Joined: Mar 2005
Posts: 1,198
Chesapeake, VA
Anywhere with potentially high fault current requires bolt-on, because the electromagnetic forces in a full-blown short-circuit fault can be enough to tear cables right out of set screws, and breakers right off the panel.

If you're just fed from a small transformer (ala residential size) or otherwise have low availible fault current, then it's less of an issue.


#173726 - 01/17/08 10:12 AM Re: Botl in or stab in? [Re: SteveFehr]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
I agree with the rest of the guys that in most cases I prefer a bolted connection.

That said:
The Square D "I-Line" breaker, their premium offering, is a plug in.

[Linked Image]



The lowly ITE-Bulldog Pushmatic is a bolt on breaker.

[Linked Image]

laugh




Member Spotlight
The_Lightman
The_Lightman
Orlando, Fl, USA
Posts: 49
Joined: August 2001
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 15 (0.004s) Memory: 0.7667 MB (Peak: 0.9085 MB) Zlib enabled. Server Time: 2017-03-28 14:01:52 UTC