master66 Offline
Member
Registered: 04/18/02
Posts: 257
Loc: Masontown, PA, USA
We were working at a factory installing 120V circuits for receptacles. While we were there we noticed that one of thier ex-plant electricians had done the same in the past only he used (1) #8 Thhn conductor as a neutral for (4) 120V circuits from a 120/240V single phase panel. There were two circuits on each phase. I know that this is not right but I can't think of any specific code section that this violates, other than the JB is overfilled. So, can anyone tell me which section(s) this violates?

Brian
Top
Work Gear for Electricians and the Trades
#173334 - 01/07/08 05:46 PM Re: Super Neutral [Re: master66]
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
No code has been violated if he has 2ea 20 amp circuits on each leg.
Top
#173336 - 01/07/08 06:05 PM Re: Super Neutral [Re: electure]
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Brian, I agree with Electure, no code has been violated, and it is specifically allowed in 225.7(B)

Roger
Top
#173342 - 01/07/08 07:39 PM Re: Super Neutral [Re: Roger]
master66 Offline
Member
Registered: 04/18/02
Posts: 257
Loc: Masontown, PA, USA
Section 225.7(B) Applies to "Lighting Equipment Installed Outdoors". Is there a similar section regarding 120V receptacles?
Top
#173408 - 01/09/08 07:55 AM Re: Super Neutral [Re: master66]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
There was much talk a couple years ago regarding computer and electronic loads. The talk that I heard indicated using a larger neutral. I have not heard much about it lately, but it is possible that is what the ex-electrician had in mind when installing the #8?
Top
#173411 - 01/09/08 08:57 AM Re: Super Neutral [Re: master66]
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I also agree there is no violation and no safety hazard.

Originally Posted By master66
Section 225.7(B) Applies to "Lighting Equipment Installed Outdoors". Is there a similar section regarding 120V receptacles?


The real question is where does the code prohibit what was done?

It does not. smile
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#173435 - 01/09/08 05:24 PM Re: Super Neutral [Re: master66]
master66 Offline
Member
Registered: 04/18/02
Posts: 257
Loc: Masontown, PA, USA
I agree that there might not be anything specifically prohibiting the practice but I would think that if it were allowed that there should be some method of calculating the size of the neutral conductor as well as some rule pertaining to handle ties on breakers. I believe there is a change regarding handle ties in the 2008 code. (210.4(B))
What is the definition of a "Multiwire Branch Circuit"?

Brian
Top
#173439 - 01/09/08 06:10 PM Re: Super Neutral [Re: master66]
BryanInBalt Offline
Member
Registered: 05/11/07
Posts: 47
Loc: Baltimore
Originally Posted By master66
there should be some method of calculating the size of the neutral conductor Brian


The 12 wire should be adequate for the load wink
(cheap shot I know)

I think everyone is just site engineering these as they go along but when I've done it we used a #10 with 3 #12 hot.

But it may all be moot anyway since paired MC is being used in most jobs now anyway.

Right from the panel no conduit on the job at all. awful.
_________________________
Design-Build isn't supposed to mean design *as* you build.
Top
#173440 - 01/09/08 06:24 PM Re: Super Neutral [Re: BryanInBalt]
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
CMP 2 does not agree that the NEC would permit the use of this common (super) neutral. text shown in italics below was to be deleted in my proposal
Quote:
2-280 Log #2224 NEC-P02 Final Action: Reject
(215.4)
______________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Recommendation: Revise as follows:
215.4 Feeders with Common Neutral.
(A) Feeders with common Neutral Two or three sets of 3-wire feeders or two
sets of 4-wire or 5-wire feeders shall be permitted to utilize a common neutral.
(B) In Metal Raceway or Enclosure.
Where installed in a metal raceway or
other metal enclosure, all conductors of all feeders using a common neutral
shall be enclosed within the same raceway or other enclosure as required in
300.20.
Substantiation: There is no code violation in using a common neutral so the
specific provision to use one is not required.
Panel Meeting Action: Reject
Panel Statement: The panel disagrees with the submitter’s substantiation.
Section 215.4 (A) is the requirement which limits the number of feeders that
may share a common neutral.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 12
_________________________
Don(resqcapt19)
Top
#173441 - 01/09/08 06:29 PM Re: Super Neutral [Re: resqcapt19]
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Originally Posted By resqcapt19
CMP 2 does not agree that the NEC would permit the use of this common (super) neutral.


I guess if the CMPs handed out red tags they would also have to provide a code section that this installation violates. smile
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals