The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
01/17/17 07:08 PM
Re: Fabricating Guards out of Lexan?
by frank
01/17/17 04:11 PM
Would ELV branch circuits be a good idea?
by gfretwell
01/17/17 01:26 PM
Why cables look like they do
by Texas_Ranger
01/17/17 12:33 PM
100% breakers?
by Texas_Ranger
01/16/17 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 20
Webmaster 18
ghost307 12
gfretwell 12
Trumpy 12
Who's Online
1 registered (Webmaster), 0 Guests and 52 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#173320 - 01/07/08 12:56 PM distance correction factor
dcdec Offline
New Member

Registered: 01/07/08
Posts: 1
Loc: ontario, canada
I'm looking for distance correction factor for 500 Kcmil aluminum table- d3 (6) states that distance and current follow a pattern factor of 10 does this mean from 4/0 I have to go each wire size up by 10x distance and current at this cables max. nominal amperage which would 185 Amp (doesnt exist on table, 160 or 200) and this is not for a residential service , it will be 600v delta.
look forward to reply, thanks in advance

Top
2017 / 2014 NEC & Related Books and Study Guides
#173355 - 01/08/08 04:13 AM Re: distance correction factor [Re: dcdec]
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
I believe what note 6 is saying is that when a current factor is increased by 10, then the max distance of that cable is decreased by 10. As well note six is used when you cannot find a value from the charts. Also, 600V will have less voltage drop than you think. A good rule of thumb is for every 100 feet of conductor, go up one size. But to be acurate, just use the example in note 9 but insert 600 V as the divisor or you will get the wrong answer. If that still doesn't help you, just call the inspector.
_________________________
Never trust an electrician with no eyebrows!!

Top
#173991 - 01/24/08 05:42 PM Re: distance correction factor [Re: mr_electrician]
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
Because Table D3 is based on single phase, make sure that after you find out your answer, multiply the distance by 1.15 due to the fact that you said you are using 3 phase.