The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm≤ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 255 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#17318 - 11/23/02 09:12 PM Huge Main Switches
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
With a recent factory upgrade, I had the
un-enviable task of throwing the Main Isolator, back into service, and got the handle stuck half way, I heard and saw welding of the contacts inside the Isolator
(1000A@400V).
How would you go about opening or closing a
High current Isolator, have I got it all wrong?.

[This message has been edited by Trumpy (edited 11-26-2002).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#17319 - 11/24/02 08:39 AM Re: Huge Main Switches
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
What I have allways done is;

Remove as much load as possible.

When you go to throw the switch, commit to the action and close it fast and hard.

If you have a chance to examine the switch de-energised always take the opportunity to do it. Often these switches haven't been moved in years and then we expect them to operate like new. A little lubrication helps a bunch.

GJ

GJ

Top
#17320 - 11/24/02 08:40 PM Re: Huge Main Switches
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
An "ACB" is mentioned, and on the North-American continent, there are 3 types of breaker construction in that range‚ÄĒair-{frame}, insulated-case and molded-case. In my experience, air-frame breakers are generally "rackable," meaning they can be mechanically exercised/checked to operate in a test position‚ÄĒunenergized.

After the fact, I would want to determine if the fault duty was too high, and if the breaker manufacturer provided any maintenance instructions. Sounds like you were able to sidestep a potentially serious accident. Because of the breaker misoperation, it integral ground-fault protection may have been useless.

In the US, NFPA 70E {Electrical Safety Requirements for Employee Workplaces} calls for evaluation of arc-blast hazards, and appropriate personal protective equipment.

Top
#17321 - 11/25/02 09:15 PM Re: Huge Main Switches
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Sorry, the part that said ACB, should have read Isolator, this is now amended.
Have since locked off the supply and cleaned the contacts and lubed the operating mechanism, works like a charm, now.
But this was an old metal-clad unit(the norm
in Industrial installations, over here).
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#17322 - 11/26/02 02:37 PM Re: Huge Main Switches
Bjarney Offline
Moderator

Registered: 04/10/02
Posts: 2561
Loc: West-Southern Inner-Northeast ...
In the US, NEMA {nema.org} has somewhat applicable standards that are on line‚ÄĒICS2.3-1995 Annex A ‚ÄėMaintenance of Motor Controllers After a Fault Condition.‚Äô

These are basically common sense, but seem worth reviewing. Handy for establishing that endless ‚Äúpaper trail.‚ÄĚ