#17318 - 11/23/02 09:12 PM Huge Main Switches
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
With a recent factory upgrade, I had the
un-enviable task of throwing the Main Isolator, back into service, and got the handle stuck half way, I heard and saw welding of the contacts inside the Isolator
(1000A@400V).
How would you go about opening or closing a
High current Isolator, have I got it all wrong?.

[This message has been edited by Trumpy (edited 11-26-2002).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
Work Gear for Electricians and the Trades
#17319 - 11/24/02 08:39 AM Re: Huge Main Switches
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
What I have allways done is;

Remove as much load as possible.

When you go to throw the switch, commit to the action and close it fast and hard.

If you have a chance to examine the switch de-energised always take the opportunity to do it. Often these switches haven't been moved in years and then we expect them to operate like new. A little lubrication helps a bunch.

GJ

GJ
Top
#17320 - 11/24/02 08:40 PM Re: Huge Main Switches
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
An "ACB" is mentioned, and on the North-American continent, there are 3 types of breaker construction in that range—air-{frame}, insulated-case and molded-case. In my experience, air-frame breakers are generally "rackable," meaning they can be mechanically exercised/checked to operate in a test position—unenergized.

After the fact, I would want to determine if the fault duty was too high, and if the breaker manufacturer provided any maintenance instructions. Sounds like you were able to sidestep a potentially serious accident. Because of the breaker misoperation, it integral ground-fault protection may have been useless.

In the US, NFPA 70E {Electrical Safety Requirements for Employee Workplaces} calls for evaluation of arc-blast hazards, and appropriate personal protective equipment.
Top
#17321 - 11/25/02 09:15 PM Re: Huge Main Switches
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Sorry, the part that said ACB, should have read Isolator, this is now amended.
Have since locked off the supply and cleaned the contacts and lubed the operating mechanism, works like a charm, now.
But this was an old metal-clad unit(the norm
in Industrial installations, over here).
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#17322 - 11/26/02 02:37 PM Re: Huge Main Switches
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
In the US, NEMA {nema.org} has somewhat applicable standards that are on line—ICS2.3-1995 Annex A ‘Maintenance of Motor Controllers After a Fault Condition.’

These are basically common sense, but seem worth reviewing. Handy for establishing that endless “paper trail.”
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals