#172953 - 12/30/07 05:49 PM Terminating Stranded Wire
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
What do you use to terminate small gauge stranded THHN wire on circuit breakers and devices?
I usually use the T&B Sta-Kons or 3M Highland crimp terminals but have also tried those Ideal Terminuts in the past.
Just want to see what method others are using and if maybe there is something different available.

TKX
Top
Work Gear for Electricians and the Trades
#172954 - 12/30/07 05:54 PM Re: Terminating Stranded Wire [Re: KJay]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Devices and breakers are listed to accept stranded 12 and 14ga THHN
_________________________
Greg Fretwell
Top
#172959 - 12/30/07 06:50 PM Re: Terminating Stranded Wire [Re: gfretwell]
leland Offline
Member
Registered: 08/20/07
Posts: 853
Loc: Lowell area, Ma. USA
Clamps: Nothing.
T&B if I need a good (any) termination on a screw.

I'm so paranoid that even with solid, I wrap the screw. Those pressure connections seem to loosen up as I twist in the device.

K-J!! 16&0 Whata Ya think!!!!
Top
#172960 - 12/30/07 06:53 PM Re: Terminating Stranded Wire [Re: gfretwell]
BryanInBalt Offline
Member
Registered: 05/11/07
Posts: 47
Loc: Baltimore
when I am forced to pull stranded to a device and the job doesn't spec the clamp type devices... I'll use some solid when I make up the box.

I've never had to connect smaller than 12 stranded to a breaker (which will work ok).
_________________________
Design-Build isn't supposed to mean design *as* you build.
Top
#172968 - 12/30/07 10:13 PM Re: Terminating Stranded Wire [Re: BryanInBalt]
Theelectrikid Offline
Member
Registered: 04/30/04
Posts: 810
Loc: Levittown, PA
I found it helps to twist the wire counter clockwise before making the hook with stranded.

In fact, I think I learned that here on ECN from a "tips" thread. Best bit of advice I've ever found here, sure helps with my traffic lights.

Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?
Top
#172971 - 12/30/07 10:42 PM Re: Terminating Stranded Wire [Re: Theelectrikid]
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
Same here. If I must terminate a stranded conductor on a screw terminal, I grab the end of the wire and twist it so tight that it almost handles like a solid conductor.

Simply stripping a stranded conductor and wrapping it messes up the natural lay of the strands and once you tighten the screw down, you end up mashing them down. Strands end up being left out of the termination. I don't like it.

In a perfect world, I'd use T&B Sta-Kons for all stranded to screw-terminal connections but that's another story.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#172983 - 12/31/07 03:04 AM Re: Terminating Stranded Wire [Re: EV607797]
jdo1942 Offline
Junior Member
Registered: 11/13/05
Posts: 31
Loc: st. louis, mo. usa
Most of us do not realize that most devices, outlets and switches are NOT rated for stranded wire. Read the listing on the box and you'll be using solid pigtails.
Top
#172984 - 12/31/07 03:07 AM Re: Terminating Stranded Wire [Re: jdo1942]
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Originally Posted By jdo1942
Most of us do not realize that most devices, outlets and switches are NOT rated for stranded wire. Read the listing on the box and you'll be using solid pigtails.


The screw terminals of all UL listed 15 and 20 amp devices are listed for both stranded and solid building wire.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#172986 - 12/31/07 05:07 AM Re: Terminating Stranded Wire [Re: iwire]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
I seems that everyone does pretty much the same thing.
It’s true that device screw terminals are listed for stranded wire as well, but it’s sometimes a pain to wrap the wires neatly without loose strands, especially on the screw terminals of less expensive commercial spec grade and resi grade receptacles.
I will sometimes twist and then loop the stranded wire around the screw terminal as if I were looping to second device and then, after tightening, snip it off about 3/16” beyond the screw so the little piece of remaining insulation holds the strands together neatly.
However, many times in order to make things easier and to follow the UL 508a standard, I, like many other electricians, will use other approved means for terminating stranded wires as well.

UL508a Standard
A connection to a wire-binding screw shall be made as follows such that no loose strands protrude from the connection.
a) Solid wire formed into a loop at least three quarters (270 degrees) around the terminal, or
b) Stranded wire that is:
1) Soldered.
2) Connected to a terminal provided with upturned ends.
3) Connected to a terminal provided with a cup washer, or
4) Connected to a crimped pressure terminal connector or eyelet.

On circuit breakers, I personally don’t like connecting stranded conductors smaller than #10.
I’ve seen too many problems with heating and corrosion between strands with the squashing and separation that occurs with the clamp type terminals, like on SQD QO. The brands like Siemens that have a plain screw terminal seem to be worse by sometimes letting loose strands ride out the side of the screw when tightened.

JMHO
Top
#173008 - 12/31/07 09:22 AM Re: Terminating Stranded Wire [Re: KJay]
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
From the UL Guide for Receptacles for Plugs and Attachment Plugs.
Quote:
Terminals of the wire-binding screw, setscrew, or screw-actuated back wired clamping types are suitable for use with both solid and stranded building wires.
_________________________
Don(resqcapt19)
Top
Page 1 of 4 1 2 3 4 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 58 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals