#1729 - 05/23/01 08:15 AM low voltage
mechcmdr Offline
Junior Member
Registered: 05/23/01
Posts: 2
I have a hallway light that won't turn on. When I took a reading I have only 48V at the switch when I should have 120V, of course. It's probably something simple, but to someone who don't know. Any Ideas?
Top
Work Gear for Electricians and the Trades
#1730 - 05/23/01 11:03 AM Re: low voltage
Anonymous
Unregistered

>I have a hallway light that won't turn on. When I took a reading I have only 48V at the switch
It's wired to your phone line instead of your electric line.
Top
#1731 - 05/23/01 12:28 PM Re: low voltage
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
mechcmdr;
do you mean you have 120V going into, and 48V coming out of(to the light) the switch?

if so can the switch...

Dspark,
if that were true, he could dial his own number for some lights!
Top
#1732 - 05/23/01 12:35 PM Re: low voltage
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
mechcmdr,

Where are you putting the test leads when you get 48v?

Bill
Top
#1733 - 05/23/01 12:40 PM Re: low voltage
Anonymous
Unregistered

>do you mean you have 120V going into, and 48V coming out of(to the light) the switch?
If that were true, wouldn't the light at least be glowing yellow?

Bill is onto something about lead placement.
Is something else running on the circuit that is working?

I would measure DC voltage and see whether it is -48. If so, it's a phone line.

My recommendation is to replace the bulb (with 60 watts or less, of course).


[This message has been edited by Dspark (edited 05-23-2001).]
Top
#1734 - 05/23/01 01:55 PM Re: low voltage
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
mechcmdr,
What type of meter are you using?
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#1735 - 05/25/01 09:13 PM Re: low voltage
mechcmdr Offline
Junior Member
Registered: 05/23/01
Posts: 2
I took the reading across the hot and common on the switch. I'm using a Wavetek volt/ohm meter. So I am guessing I have 48V coming to the switch. I took a reading on a few of the other light swithches in the house for reference and I got 120V on them and of course I get 0V when I turn on the light. And no, It's not phone wire.
Top
#1736 - 05/25/01 10:00 PM Re: low voltage
Anonymous
Unregistered

>I took the reading across the hot and common on the switch.

That won't necessarily work.

You need to measure between the line and a ground.

It sounds like perhaps an open neutral on the circuit.

Your problem is NOT low voltage.


[This message has been edited by Dspark (edited 05-26-2001).]
Top
#1737 - 05/26/01 04:45 AM Re: low voltage
C.Urch Offline
Member
Registered: 05/23/01
Posts: 36
Loc: Kill Devil Hills, NC USA
Like DSPARK says, you need to read between the common and ground. Sounds like it is a 3-way switch which may have gone bad.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 64 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals