#172833 - 12/27/07 05:29 PM Service Pedestal next to down spout
bot540 Offline
Member
Registered: 09/14/04
Posts: 174
Loc: Vernon Hills, IL
I haven't found anything in the NEC or the power company's book of codes that prevents an underground service pedestal being installed next (12"-16")to a downspout. Has anyone failed an inspection for this? Note: the downspout discharges into a drain tile.
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Top
Work Gear for Electricians and the Trades
#172866 - 12/28/07 09:33 AM Re: Service Pedestal next to down spout [Re: bot540]
JValdes Offline
Member
Registered: 06/03/07
Posts: 301
Loc: South Carolina
Your okay. Conductors must be suitable for direct burial or if in conduit the conductors must be rated for wet locations. Like THHW.