We are working on a meat packing plant that will have a 15kV lineup of outdoor metal-enclosed load interrupter switchgear. These switches will feed pad mount transformers (underground concrete encased PVC ductbank) which will serve 480/277V main-tie-main switchboards located throughout the facility. Should we provide a spare conduit for each 15 kV feeder? Pros? Cons?
Top
Work Gear for Electricians and the Trades
#17261 - 11/22/02 04:18 PM Re: 15kV Underground - Spare Conduits
The Watt Doctor Offline
Member
Registered: 12/23/01
Posts: 435
Loc: Mont Belvieu, TX
I wouldn't provide one if it is not provided for in your contract. It's funny that you should ask because every medium voltage ductbank that I've ever been involved in had a spare conduit in it. That especially holds true for primary coming from the utility.
Hit the customer up for an extra. If they ever have a failure without an extra conduit to pull in a new feeder, they may regret having not provided one while the project is under construction.

Extra Change, Bling, bling,
Doc
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX
Top
#17262 - 11/24/02 06:37 AM Re: 15kV Underground - Spare Conduits
fedup Offline
Member
Registered: 10/26/01
Posts: 31
Loc: alabama
the major cost in installing your ductbank is in the excavation and placement of concrete.An extra 5" conduit won't add to much to the cost.If the runs are long I would intall steel 90's have seen the pull rope burn through pvc more times than I would care to say
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 90 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals