#172578 - 12/21/07 02:56 PM AFCIs and MWBCs  
Tiger  Offline
Member
Joined: May 2005
Posts: 706
Crystal Lake, IL USA
Now that it's almost 2008, I'm giving serious consideration to installing several hundred AFCIs in the coming months. I had a thought that it might not be a code violation to tie the two ungrounded conductors of a MWBC (anywhere but on the breaker itself) and terminate it on one AFCI breaker. In my rather small home these two 15-amp circuits are 18 receptacles and lights, including a bath GFCI receptacle.

Dave


2017 / 2014 NEC & Related Books and Study Guides

#172579 - 12/21/07 03:25 PM Re: AFCIs and MWBCs [Re: Tiger]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
Tiger,
I think that goes against good wiring practice regarding placing the two ungrounded conductors on opposite sides of the phase so the neutral only carries the unbalanced portion of the load as opposed to the full neutral current of both ungrounded conductors.
You would probably be safer and more code compliant, depending on the actual load, if you just used one side of the MWBC to feed all of the receptacles and lighting as one two-wire circuit.

JMHO


#175750 - 03/10/08 03:54 PM Re: AFCIs and MWBCs [Re: Tiger]  
KJay  Offline
Member
Joined: Nov 2007
Posts: 763
MA, USA
I see from their literature that Siemens now makes a two-pole combination AFCI cb for this type of application.
This is what I will need to use for my second floor bedroom circuits when the time comes as they were also wired with 14/3.
There may be other manufacturers making two-pole combination AFCI cb’s, but not sure.