The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
gfretwell 13
Trumpy 13
Who's Online
1 registered (electure), 0 Guests and 191 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#17244 - 11/22/02 09:20 AM 100amp service in a 3400 ftsq home?
cdimarco Offline
Junior Member

Registered: 11/22/02
Posts: 1
Loc: NYC, NY USA
Is there a code that a house of a certain size needs to be equipped with a certain type of electrical service?

Looking at a new house whose standard service is 100 amps. In order to upgrade any electric in the house - multiple high hats, electric ovens, christmas lights, pool, the home will certianly require more powerful service like 150 or 200a service.

Is this the builders or purchasers responsibility on a home this size?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#17245 - 11/22/02 10:22 AM Re: 100amp service in a 3400 ftsq home?
mj Offline
Member

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
general lighting, 3 volt/amps per sq ft 3400 3 is 10200 va ,is 42.5 amps, you have to add all your appliance loads, heat or ac, the largest of the two. when you add in all the factors you will need at the least 150 service . see art 220, for calcalations examples

Top
#17246 - 11/22/02 11:49 AM Re: 100amp service in a 3400 ftsq home?
watthead Offline
Member

Registered: 10/13/01
Posts: 182
Loc: South Carolina
If you had gas appliances and heat are you sure it would calculate to 150 amp minimum? I think what is most important in this situation is that the NEC is not a design manual, and its minimum requirements do not always provide an adequate installation, only one esentially free of hazards. The extra cost of the larger service in a house of that size would be quickly amortized. Install a 200 amp minimum service.

Top
#17247 - 11/23/02 06:18 PM Re: 100amp service in a 3400 ftsq home?
falcondfb Offline
Member

Registered: 09/28/02
Posts: 37
Loc: Jersey, USA
i am doing work in a 6000sq' house w/ a 200amp service. elec dryer, oven hot tub outside, 76 amps of a/c, 7 refers, etc and we are finishing the basement to add another 2000 ft. service is underground 300 ft away and x-former in on other side of driveway and cobblestone walkway that was just done. BTY house is just 3 months old. can't wait to give them a price for service upgrade.