The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 293 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#17244 - 11/22/02 09:20 AM 100amp service in a 3400 ftsq home?
cdimarco Offline
Junior Member

Registered: 11/22/02
Posts: 1
Is there a code that a house of a certain size needs to be equipped with a certain type of electrical service?

Looking at a new house whose standard service is 100 amps. In order to upgrade any electric in the house - multiple high hats, electric ovens, christmas lights, pool, the home will certianly require more powerful service like 150 or 200a service.

Is this the builders or purchasers responsibility on a home this size?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#17245 - 11/22/02 10:22 AM Re: 100amp service in a 3400 ftsq home?
mj Offline

Registered: 06/10/02
Posts: 188
Loc: meriidian, ms
general lighting, 3 volt/amps per sq ft 3400 3 is 10200 va ,is 42.5 amps, you have to add all your appliance loads, heat or ac, the largest of the two. when you add in all the factors you will need at the least 150 service . see art 220, for calcalations examples

#17246 - 11/22/02 11:49 AM Re: 100amp service in a 3400 ftsq home?
watthead Offline

Registered: 10/13/01
Posts: 182
Loc: South Carolina
If you had gas appliances and heat are you sure it would calculate to 150 amp minimum? I think what is most important in this situation is that the NEC is not a design manual, and its minimum requirements do not always provide an adequate installation, only one esentially free of hazards. The extra cost of the larger service in a house of that size would be quickly amortized. Install a 200 amp minimum service.

#17247 - 11/23/02 06:18 PM Re: 100amp service in a 3400 ftsq home?
falcondfb Offline

Registered: 09/28/02
Posts: 37
Loc: Jersey, USA
i am doing work in a 6000sq' house w/ a 200amp service. elec dryer, oven hot tub outside, 76 amps of a/c, 7 refers, etc and we are finishing the basement to add another 2000 ft. service is underground 300 ft away and x-former in on other side of driveway and cobblestone walkway that was just done. BTY house is just 3 months old. can't wait to give them a price for service upgrade.