#172183 - 12/15/07 10:09 AM Energy savings from magnetic to electronic ballast
ayrton Offline
Member
Registered: 12/21/01
Posts: 201
Loc: Pa
Does anybody know the formula for calculating energy savings from switching Magnetic ballasts and lamps, over to electronic ballasts and lamps for 2x4 lay in troffers.

For arguments sake, lets say 4 lamp fixture w/ 34 or 40w lamps magnetic

And 4 lamps 32 watts electronic
Top
Work Gear for Electricians and the Trades
#172185 - 12/15/07 10:29 AM Re: Energy savings from magnetic to electronic ballast [Re: ayrton]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
raob x volts x nof - ranb x volts x nof

where:

raob - rated amps of old ballast
volts - duh
nof - number of fixtures
ranb - rated amps of new ballast
_________________________
"Live Awesome!" - Kevin Carosa
Top
#172187 - 12/15/07 10:59 AM Re: Energy savings from magnetic to electronic ballast [Re: sparkyinak]
LarryC Offline
Member
Registered: 07/05/04
Posts: 780
Loc: Winchester, NH, US
How about the reduction in heat generated?
Top
#172190 - 12/15/07 11:19 AM Re: Energy savings from magnetic to electronic ballast [Re: LarryC]
sparkyinak Offline
Member
Registered: 07/08/07
Posts: 1307
Loc: Alaska
If it is a massive building then yes you could figure it in. I might have info on that. I will see If I can locate it. Living in AK, you do not really think of that since we only use AC in our IT rooms. Most buildings I deal with are for the most part are well insulated Any heat loss form the lights that is picked up by the heating systems would me insignicant.


Edited by sparkyinak (12/15/07 11:20 AM)
_________________________
"Live Awesome!" - Kevin Carosa
Top
#172195 - 12/15/07 01:40 PM Re: Energy savings from magnetic to electronic ballast [Re: sparkyinak]
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Let me put it this way .... when I converted an office building from T-12's with conventional ballasts, to T'8's with electronic ballasts .... the math gave me a very conservative number! IIRC, I was expecting savings of about $250/ month .... while the actual saving was nearly $400/mo.

Actual amp readings, before and after, showed about a 35% reduction in current drawn. This is not considering the lesser load on the air conditioning, due to the lower operating temperature.

I was changing things 'bulb for bulb.' If you are replacing 4 lamp fixtures with 3 lamp fixtures, expect further savings.
Top
#172229 - 12/16/07 09:50 AM Re: Energy savings from magnetic to electronic ballast [Re: renosteinke]
ayrton Offline
Member
Registered: 12/21/01
Posts: 201
Loc: Pa
I was thinking more of this formula

# of luminares x total W per luminare x Annual operating hrs x Energy cost per KWH= First year energy cost/1000

Knowing amperage is not accurate enough. There is input amps and out put amps. Example, a 400w MH fixture has a total input of about 465W Amperage on ballast is not accurate in my experience. Need to measure True Power (watts)


Edited by ayrton (12/16/07 09:52 AM)
Top
#172234 - 12/16/07 10:39 AM Re: Energy savings from magnetic to electronic ballast [Re: ayrton]
Jim M Offline
Member
Registered: 08/10/01
Posts: 457
Loc: Chestertown, MD, USA
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals