According to the wire table 310-16 ( 99 Code Book, I don't have my new book with me) # 8 wire is good for 50 amps in the 75 degree column, and I know this is good only if the terminals are rated 75 degrees, which they are. Does
8/3 with ground romex qualify for this rating also? I had an inspector tell me once that it didn't, but I can't find where he would have got that from unless it was in an old code at the time. Thanks, Steve...
Top
Work Gear for Electricians and the Trades
#172031 - 12/11/07 06:30 AM Re: 8/3wg romex [Re: sparkync]
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
He is maybe refering to 334.80, which limits the ampacity of NM cables to that of the 60 degree column.
_________________________
Earl
Top
#172034 - 12/11/07 08:37 AM Re: 8/3wg romex [Re: earlydean]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Yup that is what he is talking about and you can't get away with the "round up" trick you can with #6 since 40 is a standard breaker size. Even if you decide to go for SE/SER you still can't use the 75c column because of 338.10(B)(4)
_________________________
Greg Fretwell
Top
#172072 - 12/11/07 07:45 PM Re: 8/3wg romex [Re: gfretwell]
KJay Offline
Member
Registered: 11/27/07
Posts: 763
Loc: MA, USA
Hi Greg,
I could be wrong, but I thought 338.10(B)4 excluded 334.80 Ampacity. confused
Top
#172079 - 12/11/07 09:36 PM Re: 8/3wg romex [Re: KJay]
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You are right. I should try to read a little better before I speak. My original thought was that it was OK, then I looked it up. wink
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 30 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals