The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Locked rotor, no burnout
by andey
Today at 04:48 AM
Temporarily feeding a panel...
by Potseal
Yesterday at 11:05 PM
Massive power outage South Australia
by Meadow
Yesterday at 06:46 AM
short circuit??
by Meadow
Yesterday at 06:43 AM
Norwegian power?
by Meadow
Yesterday at 06:36 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Potseal 7
Who's Online
1 registered (jraef), 292 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#171772 - 12/05/07 05:41 AM Secondary conductor size for transformers
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Hello, can someone tell me the rule for sizing secondary conductors of a dry type transformer. I know it is 125% minimum, but what rule is it when you do not have secondary protection and you are sizing your panel board based on
14-606(2)
Thanks
_________________________
Never trust an electrician with no eyebrows!!

Top
2014 / 2011 NEC & Related Books and Study Guides
#171773 - 12/05/07 06:03 AM Re: Secondary conductor size for transformers [Re: mr_electrician]
Rick Kelly Offline
Member

Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
14-100(d) comes to mind...

Top
#171780 - 12/05/07 12:07 PM Re: Secondary conductor size for transformers [Re: mr_electrician]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I think you have it covered there, 26-256 for the 125%, but that is maximum, not minimum.

Top
#171783 - 12/05/07 12:53 PM Re: Secondary conductor size for transformers [Re: jay8]
bill woods Offline
Member

Registered: 11/21/01
Posts: 45
Doesn't 26-256 cover overcurrent protection? Aren't we talking about conductor size here? Shouldn't we be looking at 26-258? If you install overcurrent devices in the primaries, and these devices limit the current on the secondaries to an amperage less than the KVA rating of the transformer allows don't you size the secondary conductors to this value?

Top
#171785 - 12/05/07 02:13 PM Re: Secondary conductor size for transformers [Re: bill woods]
Rick Kelly Offline
Member

Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
I take back my earlier mention of 14-100(d) for the following reason.

14-100(d) can not apply as its subrule (ii) requires that the circuit teminate at a single overcurrent device, which in this case we do not have.

So it looks like...

As per rule 26-258(2a) the minimum ampacity of the secondary conductors must be sized at 125% of the transformer's rated secondary current.

Good catch Bill, your comment made me rethink this.

Top
#171814 - 12/06/07 08:08 AM Re: Secondary conductor size for transformers [Re: Rick Kelly]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
Yes, oops, I read that as overcurrent when the post mentioned not using secondary protection, so that would be 125% minimum on conductor size.
But Bill, the wording on 26-256 refers to rated current of the transformer, so you wouldnt limit current on the secondary conductors to less than the KVA rating of the transformer unless you wanted to do so, since 125% is the maximum, you could go less if you chose to.

Top
#171859 - 12/07/07 04:21 AM Re: Secondary conductor size for transformers [Re: mr_electrician]
mr_electrician Offline
Member

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Thanks guys for taking the time on this subject. I was talking with the local inspector and he said it like this....125% of full load current on the secondary when there is no protection on the secondary (what rule is that?). So even when your choking transformers you would size your secondary conductors based on 14-100(f)(ii) and multiply by 125%
Example: A 45KVA can put out 115 amps when the primary is fused at 40Amps. Now if I were to choke the transformer and fuse the primary at 30Amps, then the secondary conductors would be sized for 108A (30 X 2.88 X 1.25 = 108)
Clear as mud!