#171496 - 11/29/07 09:05 AM hot tub
watersparkfalls Offline
Member
Registered: 03/08/05
Posts: 212
Loc: Washington...Not DC
disco within sight refers to commercial installs if memory serves.
i want to put a residential disco around the corner of the house, which clearly it wont be anywhere near "in sight"
it will be a cleaner install with less pipe on the outside(retro/remodel) of the house and more in the dirt.
sound complient?
thanks,
H2O
Top
2017 / 2014 NEC & Related Books and Study Guides
#171498 - 11/29/07 09:49 AM Re: hot tub [Re: watersparkfalls]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Commercial spas and hot tubs require an emergency stop. That is separate and different than the disconnect within site of motors which is required in residential too
_________________________
Greg Fretwell
Top
#171586 - 12/01/07 07:51 AM Re: hot tub [Re: gfretwell]
drum Offline
Member
Registered: 09/29/07
Posts: 14
Loc: USA
The few residential hot tubs I have wired I used a spa disconnect which has the GFCI breaker inside it. I installed it futher than 5ft but within site of the tub. After looking at 680.41 I am a bit confused. It says this requirement shall not apply to single family dwellings???? Does this mean the GFCI breaker could go in the main panel and pipe right out to the tub? Maybe a emergency switch for Spa's and Hot Tubs is somthing different???
Top
#171591 - 12/01/07 09:19 AM Re: hot tub [Re: drum]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
The emergency stop is for the user or rescuer. The disconnect is for service personel. Different things.
The disconnect removes all power, the emergency stop only needs to stop the motors. It is possible to make this one switch but that is not usually how commercial systems work. If nothing else, the emergency stop usually leaves the light on. I have seen some old systems that only turned off the jet pump (the low speed circulation pump and heat kept running) but that is not really legal.
_________________________
Greg Fretwell
Top
#171609 - 12/01/07 05:31 PM Re: hot tub [Re: gfretwell]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
The code reference for the Maintenance Disconnect is 680.12 and this Disconnect must be within sight (you can see it and it's not more than 50 feet away) and it needs to disconnect everything except the lighting. It is not required to be located more than 5 feet from the tub if it is located under the skirt of the tub and not accessible from the persons in the tub. This was hotly discussed at an IAEI seminar in Michigan with Mike Johnston making the statement about the use of the disconnect under the skirt of the tub as being code compliant.
_________________________
George Little
Top
#171612 - 12/01/07 06:37 PM Re: hot tub [Re: George Little]
drum Offline
Member
Registered: 09/29/07
Posts: 14
Loc: USA
Thanks for pointing out 680.12 George
I appriciate everyones help
Top
#171619 - 12/01/07 11:03 PM Re: hot tub [Re: George Little]
frenchelectrican Offline
Member
Registered: 02/06/03
Posts: 939
Loc: Wi/ Paris France { France for ...
Originally Posted By George Little
The code reference for the Maintenance Disconnect is 680.12 and this Disconnect must be within sight (you can see it and it's not more than 50 feet away) and it needs to disconnect everything except the lighting. It is not required to be located more than 5 feet from the tub if it is located under the skirt of the tub and not accessible from the persons in the tub. This was hotly discussed at an IAEI seminar in Michigan with Mike Johnston making the statement about the use of the disconnect under the skirt of the tub as being code compliant.


I am suprised with that what Mike Johnston did say that IMO i dont like the idea have the disconnect under the skirting becase some of the skirting have screw in panel and need screw driver to take it off.

i rather have it exteral location so i can turn it off before i can open the tub panel.

Merci, Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 124 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals