#171464 - 11/28/07 06:54 PM Conduit Body Fill  
poorboy  Offline
Member
Joined: Jun 2005
Posts: 124
Central Maine
Running 4-4inch IMC from a pad mount xformer up the side of a building to a 480 volt 1600 Amp main switch in a second floor electrical room. There will be 4-600 MCM THHN's in each.

The 4 inch LB's (not the extra length ones) say inside they are good for 3-4/0's. Is that all you can fit in 40% of this LB??? I was surprised by this, but had a bit of trouble finding the answer in the 05 NEC.

Probably will have to use a huge weatherproof box (CT Cabinet) to make the transition and run all 4 pipes thru it. Then nipple out the back to the Main Switch.

It is also surprising how hard it is to come in the side of this switch with 4-4 inch conduits...the frame bracing is in the middle of the side panel. 16-600's will be a formidible task.


2017 / 2014 NEC & Related Books and Study Guides

#171467 - 11/28/07 08:24 PM Re: Conduit Body Fill [Re: poorboy]  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
The answer is in 314.28, which applies to not only boxes, but conduit bodies used as pull boxes.
6 times the size of the conduit for angle pulls.


The wording IMO is unclear, referring in A(1)and (2)only to "boxes" and then adding the conduit bodies in the "exception".

314.28(3) addresses the conditions under which a smaller conduit body can be used....it has to be marked with the maximum allowable number and size of conductors.(thus the 3-4/0 marking)





#171472 - 11/28/07 10:09 PM Re: Conduit Body Fill [Re: electure]  
WireNuts29  Offline
Member
Joined: Jul 2007
Posts: 85
Mass, U.S.A.
From expierience, skip the Lb's on any wiring above 350 mcm. It is worth the saved labor trying to wrestle 4 600's into.Especially 4 conduits worth. Get a Utility aproved cabinet.


#171487 - 11/29/07 06:24 AM Re: Conduit Body Fill [Re: WireNuts29]  
poorboy  Offline
Member
Joined: Jun 2005
Posts: 124
Central Maine
I agree on skipping the LB's as a general rule. I have used appropriately sized wireways in indoor locations for years. They are much cheaper and in a 2 or 3 foot length so forgiving with large conductors.

The owner in this case was looking for the neatness of the final installation which would result from LB's but it I now see just can't happen---will have to be a CT cabinet or similar.




Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,137
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.014s Queries: 15 (0.003s) Memory: 0.7588 MB (Peak: 0.8904 MB) Zlib enabled. Server Time: 2017-03-26 01:36:53 UTC