The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by HotLine1
52 minutes 53 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 215 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#171436 - 11/28/07 04:40 AM Panel as a raceway
sudsy4 Offline
Member

Registered: 04/24/02
Posts: 32
Loc: Elizabeth,PA USA
I am increasing the service at a commercial retail store from 1200amp to 3000amp. We are installing the new service equipment directly outside from the existing, some of the circuits from the existing will be fed from the new. Can I use the existing panel as a wireway to the new panel if the space in the panel permits? The two panels will be joined by 4inch nipples through the backs.

Thanks for any help

Bill
_________________________
Bill

Top
2014 / 2011 NEC & Related Books and Study Guides
#171459 - 11/28/07 12:17 PM Re: Panel as a raceway [Re: sudsy4]
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Among a great number of other things, Section 408.2 requires panelboards to also comply with Article 312.
Section 312.8 requires enclosures for OC devices to provide adequate space for conductors feeding through or tapping off by filling the wiring space at any cross section to no more than 40% fill for conductors, and the conductors, splices and taps no more than 75% of the cross sectional area of that space.

If you have the room, then the existing panel can be used to splice extensions into the new panel.
_________________________
Earl

Top
#171494 - 11/29/07 08:15 AM Re: Panel as a raceway [Re: earlydean]
JValdes Offline
Member

Registered: 06/03/07
Posts: 308
Loc: South Carolina
Yes, again. Take out all the guts.

Top
#171499 - 11/29/07 11:57 AM Re: Panel as a raceway [Re: JValdes]
sudsy4 Offline
Member

Registered: 04/24/02
Posts: 32
Loc: Elizabeth,PA USA
Thanks for the help, I was pretty sure it was OK but was unsure of the code section; 312.8 was what I needed to convince the owner.

Thanks again
_________________________
Bill

Top