The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
49 minutes 28 seconds ago
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 248 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#171424 - 11/27/07 06:59 PM Choking Transformers
mr_electrician Offline

Registered: 06/22/07
Posts: 106
Loc: London, Ontario
Hello, can someone tell me what it means to choke a transformer and the theory behind it. When would you do this and why?
Never trust an electrician with no eyebrows!!

2014 / 2011 NEC & Related Books and Study Guides
#171439 - 11/28/07 06:12 AM Re: Choking Transformers [Re: mr_electrician]
ghost307 Offline

Registered: 05/09/05
Posts: 883
Loc: Chicago Illinois USA
The OCP requirements give the maximum rating that can be used to protect a transformer.

In the case of a recent design here, the load was just beyond the capacity of a 300KVA transformer, but the next size is 500KVA.
In order to avoid the costs and physical size of the OCP on both sides of the transformer, it was fused at something less that the Code maximum. Since that will also limit the secondary side current, the smaller distribution equipment can be used on that side as well. I rarely choke a transformer, but sometimes the big jump in sizes for the big ones get to be problems. In this case, I would have needed a 350KVA transformer (if anybody sold one), but I was able to choke a 500KVA without having to use the maximum OCP sizes in the design.