The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
breaker meltdown
by sparky
Yesterday at 07:30 PM
230 or 345 kV transmission lines?
by Vlado
09/24/16 09:33 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 14
sparky 10
gfretwell 8
sparky66wv 8
Vlado 6
Who's Online
1 registered (Radar), 249 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#171416 - 11/27/07 02:20 PM section 18 CEC
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
I am not well versed on this section of the code, especially the 20th edition. What would be the classification of a room with a 40, 000 litre tank storing # 2 fuel oil be? IE this is diesel, so I dont know if with the flash point of diesel, the area isnt a hazardous location.
It seems that a room with a diesel genset is not a hazardous location either, and you are pretty much certain fuel is being stored there.

Top
2014 / 2011 NEC & Related Books and Study Guides
#171502 - 11/29/07 01:31 PM Re: section 18 CEC [Re: jay8]
Rick Kelly Offline
Member

Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
#2 heating oil is not considered a volatile substance as its flash point is very high, 52 degrees C. Locations where it is stored is not considered a hazardous location for the requirements of sections 18 and 20 of the CEC.

Top
#171634 - 12/02/07 08:07 AM Re: section 18 CEC [Re: Rick Kelly]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
Thanks Rick, are you referencing a rule on flash point? I checked sections 18 and 20 and also the appendix, and did not find diesel/#2 heaing oil mentioned, so I assume it is not part of those sections.

Top
#171647 - 12/02/07 10:56 AM Re: section 18 CEC [Re: jay8]
SP4RX Offline
Member

Registered: 10/01/07
Posts: 56
Loc: Edmonton, Alberta, Canada...eh
Hi Jay.
If section 18 applies to diesel, it would have to be a Class 1 location as per 18-004 (a)---"Class 1 locations are those in which flammable gases or vapours are or may be present in the air in quantities sufficient to produce explosive gas atmospheres"

So I guess the question is whether diesel produces flammable gases "in quantities sufficient to produce explosive gas atmospheres".

Looking at the table in appendix B (18-066), I see that diesel is not listed. However, looking at fuel oil #2 msds sheets (section 5), it would appear that diesel does indeed give off explosive vapours.

I would think that 18-006-(c)-(ii) would apply, as you have "flammable volatile liquids...normally confined within closed containers...can escape only as a result of accidental rupture or breakdown..."

Just my $0.02


Shawn.

Top
#171667 - 12/02/07 06:44 PM Re: section 18 CEC [Re: SP4RX]
leland Offline
Member

Registered: 08/20/07
Posts: 856
Loc: Lowell area, Ma. USA
Not technical.. well maybe. Mythe Busters, Did a show on a leaking gas tank catching up to a speeding away vehicle and blowing up. That didn't happen, The gas stayed up to speed at about 3 MPH.
Then the diesel test: Even slower and they had a difficult time even getting the vapors to ignite.

For what it's worth. (Just a lighter momment)

Top
#171688 - 12/03/07 07:33 AM Re: section 18 CEC [Re: leland]
Rick Kelly Offline
Member

Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
NFPA 497 - "Recommended Practice for the Classification of Flammable Liquids, Gases, or Vapors and of Hazardous (Classified) Locations for Electrical Installations in Chemical Process Areas". Defines a "Flammable Liquid" as one that has a flash point lower then 100 degF.

This means Diesel or #2 heating oils, with a flash point of 152 degF, is a "combustible liquid" and not a "flammable" one. And as such, CEC sections 18 & 20 clearly do not apply to a combustible liquid, only a flamable one.

Here is a link with some reading on the subject... While this is a link that is based on the NEC, the situation is the same.

http://www.mikeholt.com/codeforum/ultimatebb.php?ubb=get_topic;f=22;t=000043

Top
#171781 - 12/05/07 12:11 PM Re: section 18 CEC [Re: Rick Kelly]
jay8 Offline
Member

Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
Again thanks. You have to do a bit of digging for it, but it appears section 18 and 20 do refer to flammable liquids and combustible dusts, I dont see combustible liquids.

Top