#17123 - 11/20/02 05:24 PM WIRE AMPACITY
mike knight Offline
Junior Member
Registered: 10/11/02
Posts: 5
does anyone size wire by article 110-14c? temp limitations under 100 amps to the ampacity from the 60 degree celius column of artical 310-16 no matter what kind of wire. over 100 amps is the 75 C column.
Top
Work Gear for Electricians and the Trades
#17124 - 11/20/02 07:01 PM Re: WIRE AMPACITY
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
yes
_________________________
Don(resqcapt19)
Top
#17125 - 11/20/02 09:16 PM Re: WIRE AMPACITY
Jacuzzi Guy Electric Offline
Member
Registered: 10/25/02
Posts: 33
Loc: Dearborn Heights Michigan Unit...
So, what are you trying to wire? And what is the ambient temperature around?
Top
#17126 - 11/20/02 10:00 PM Re: WIRE AMPACITY
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
This term ampacity is rather curious, is this a commonly used term in the US?.
I assume you mean current-carrying capacity of a conductor?.
Not meaning to pin-prick.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#17127 - 11/21/02 03:51 AM Re: WIRE AMPACITY
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
110-14 needs to be adhered to.
The 90 deg. columns can be used for derating purposes.
Top
#17128 - 11/21/02 06:05 AM Re: WIRE AMPACITY
Matt M Offline
Member
Registered: 03/25/01
Posts: 93
Loc: Laporte, MN, USA
I agree with the others.

If all of the involved equipment is not listed and marked otherwise, on circuits rated 100 amps or less, or marked for #14 AWG through #1 AWG conductors, you must use the ampacities listed in the 60 degree column as outlined in 110.14c1a, regardless of the temperature rating of the conductor that you are using.

Matt
Top
#17129 - 11/21/02 06:50 AM Re: WIRE AMPACITY
Matt M Offline
Member
Registered: 03/25/01
Posts: 93
Loc: Laporte, MN, USA
Trumpy,

The word ampacity is legitimate.

The NEC defines it as : "The current, in amperes, that a conductor can carry continuously under the conditions of use without exceeding its temperature rating".

[This message has been edited by Matt M (edited 11-21-2002).]
Top
#17130 - 11/21/02 08:26 AM Re: WIRE AMPACITY
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Quote:
This term ampacity is rather curious, is this a commonly used term in the US?.
I assume you mean current-carrying capacity of a conductor?.

Trumpy,
Ampacity is not a term we're used to seeing in the British-influenced part of the English-speaking world, but it's used widely in the United States.

I like the term: It's a neat and much quicker way of saying "current-carrying capacity" or even "current rating."
Top
#17131 - 11/21/02 06:08 PM Re: WIRE AMPACITY
George Offline
Member
Registered: 02/23/02
Posts: 375
I usually use the 75 degree col for 75 degree wire used in feeders. The breakers at both ends are rated at 75 degrees.
Top
#17132 - 11/23/02 06:40 PM Re: WIRE AMPACITY
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Must say I agree Paul,
its a very "round" sounding word.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 36 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals