The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
230 or 345 kV transmission lines?
by Vlado
Yesterday at 09:33 AM
breaker meltdown
by crselectric
Yesterday at 12:42 AM
Electrical mast flashing product
by ThomasWinfrey
09/22/16 12:14 AM
What estimating software do you recommend?
by sparky
09/21/16 07:20 PM
"Dry Run" Inspection goes awry
by HotLine1
09/20/16 07:39 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
HotLine1 17
gfretwell 9
sparky 9
sparky66wv 8
Vlado 6
Who's Online
0 registered (), 284 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#171095 - 11/19/07 03:41 PM Current carrying conductor
GTE Offline
Member

Registered: 03/26/03
Posts: 48
Loc: Bridgehampton, N.Y. USA
Where in the code does it say that the grounded conductor of a 2-wire circuit is counted as a current carrying conductor?

Top
2014 / 2011 NEC & Related Books and Study Guides
#171099 - 11/19/07 05:44 PM Re: Current carrying conductor [Re: GTE]
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5299
Loc: Blue Collar Country
Does it need to? It seems patently obvious that if you get a reading on an amp clamp, it's a current carrying conductor.

Top
#171107 - 11/19/07 06:51 PM Re: Current carrying conductor [Re: GTE]
Raymfl Offline
Member

Registered: 09/20/07
Posts: 12
Loc: Seminole County, FL
 Originally Posted By: GTE
Where in the code does it say that the grounded conductor of a 2-wire circuit is counted as a current carrying conductor?


Is this in reference to derating for the number of conductors in a conduit? If it is see 310.15(B)4


Edited by Raymfl (11/19/07 06:55 PM)

Top
#171123 - 11/20/07 05:22 AM Re: Current carrying conductor [Re: Raymfl]
ghost307 Offline
Member

Registered: 05/09/05
Posts: 876
Loc: Chicago Illinois USA
If the current travels to the load on the phase wire, the only path that it can use to get back to the source is the other conductor.
QED
_________________________
Ghost307

Top
#171134 - 11/20/07 10:23 AM Re: Current carrying conductor [Re: ghost307]
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
For a 2-wire circuit, the circuit is always going to be unbalanced, and the neutral considered a current carrying conductor per 310.15(B)(4)(a).


Edited by SteveFehr (11/20/07 10:23 AM)

Top
#171198 - 11/21/07 07:06 PM Re: Current carrying conductor [Re: SteveFehr]
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
No "Neutral" in a 2 Wire Circuit.

Same level of Current will flow on both Conductors -
(unless something is terminated incorrectly!..) \:o

The same applies to:
  1. L-N 120 Volt 2 Wire Circuits, from a 1 Phase 3 wire source,
  2. L-N 120 Volt 2 Wire Circuits, from a 3 Phase 4 wire Wye source,
  3. L-N 120 Volt 2 Wire Circuits, from a 3 Phase 4 wire Delta source,
  4. L-N 277 Volt 2 Wire Circuits, from a 3 Phase 4 wire Wye source,
  5. L-L 208 Volt 2 Wire Circuits, from a 1 Phase 3 wire source,
  6. L-L 208 Volt 2 Wire Circuits, from a 3 Phase 3 wire source,
  7. L-L 208 Volt 2 Wire Circuits, from a 3 Phase 4 wire source,
  8. L-L 240 Volt 2 Wire Circuits, from a 1 Phase 3 wire source,
  9. L-L 240 Volt 2 Wire Circuits, from a 3 Phase 3 wire source,
  10. L-L 240 Volt 2 Wire Circuits, from a 3 Phase 4 wire Delta source,
  11. L-L 480 Volt 2 Wire Circuits, from a 3 Phase 3 wire source,
  12. L-L 480 Volt 2 Wire Circuits, from a 3 Phase 4 wire source,
  13. L-L-L 208 Volt, 240 Volt and 480 Volt 3 Wire Circuits, from a 3 Phase 3 or 4 wire source.


Just wanted to make the subject clear.

Scott

BTW, I think it's time to draw up some basic circuit schematics, to demonstrate the flows + levels on 2 wire circuits
(also point out when a Common Grounded Conductor is a "Balanced Neutral", and when it isn't).