#170851 - 11/13/07 05:12 PM Hospital emergency power circuit
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
I need some input from those with experience in hospital wiring. I have been asked to install some receptacles in the patient care rooms in the emergency room. The receptacles are for new computer interface equipment, and are to be installed on the wall aproximately six inches from the ceiling. They also want them on emergency / generator power. My question is whether the health care facility mc cable is adequate for the installation, or would emt be required?

Thanks for your input.
Top
2017 / 2014 NEC & Related Books and Study Guides
#170855 - 11/13/07 05:19 PM Re: Hospital emergency power circuit [Re: watthead]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Your choice- either would satisfy 517. They probably will need the redundant ground. I would look an see what the print calls out. Don't mean to be an educated donkey here but the plans have the last word.
_________________________
George Little
Top
#170858 - 11/13/07 05:39 PM Re: Hospital emergency power circuit [Re: George Little]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
I;d advise you to Read 517.30 C (3) Handbook explains it well.
Top
#170859 - 11/13/07 05:49 PM Re: Hospital emergency power circuit [Re: Yoopersup]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Ernie- He can add 517.13 to the answer too.
_________________________
George Little
Top
#170862 - 11/13/07 06:00 PM Re: Hospital emergency power circuit [Re: George Little]
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
George
517.30 C (3) refers you to 517.13A & 517.13 (B)
But it also lists only 4 areas where Listed Flexable Metal raceways CAN be used. 517.30 C (3)(3)
Top
#170869 - 11/13/07 06:51 PM Re: Hospital emergency power circuit [Re: Yoopersup]
George Little Offline
Member
Registered: 01/18/04
Posts: 1488
Loc: Michigan USA
Thanks Ernie- I learned something.
_________________________
George Little
Top
#170871 - 11/13/07 06:57 PM Re: Hospital emergency power circuit [Re: Yoopersup]
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
Thanks guys. I had looked at both of those Code sections, but was still not exactly sure if I could sneak the HCF-mc in under 517.30(C)(3)(3)c. I am now looking for my handbook. There are no plans or drawings on this one, only a quick walk thru with we want one here and here,and I am supposed to remember the 18 or is it 19 locations. thanks again.
Top
#170876 - 11/13/07 07:25 PM Re: Hospital emergency power circuit [Re: watthead]
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
It looks like I will be using emt on this one to cma. Hospital says they don't care which way as long as it is done to code.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals