#170821 - 11/12/07 05:17 PM Grounded B phase
sparky 134 Offline
Member
Registered: 09/04/04
Posts: 91
Loc: Joliet, Il, USA
I received a phone call today from an HVAC contractor who was in the process of changing out the compressor in a RTU which was fed with a grounded B phase system. He wanted to know if he could install a 3phase monitor that would prevent his compressor from running on single phase if the unit lost a phase.

I have never had the "pleasure" of working on a grounded B phase system so I didnt' have an answer for him. He said he had changed this compressor out 1.5 years ago and it had already died.

So I started thinking.....would the compressor for this type of electrical system be different from one used on a modern 3phase system ? Could the grounded B phase be the cause of the compressor failing so soon if the compressor wasn't designed for use on a grounded B phase system ?

Top
Work Gear for Electricians and the Trades
#170825 - 11/12/07 06:31 PM Re: Grounded B phase [Re: sparky 134]
gfretwell Online   content


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
There is nothing special about corner delta that you wouldn't have in red leg delta. Anything that works on centertapped delta should work on corner delta (except 120v loads)
He does know this is 240, not 208?
_________________________
Greg Fretwell
Top
#170827 - 11/12/07 08:13 PM Re: Grounded B phase [Re: sparky 134]
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
Originally Posted By sparky 134
I received a phone call today from an HVAC contractor who was in the process of changing out the compressor in a RTU which was fed with a grounded B phase system. He wanted to know if he could install a 3phase monitor that would prevent his compressor from running on single phase if the unit lost a phase.


He doesn't need a different motor (which does not exist), he needs a Phase Loss Relay added to his starter control circuit instead.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals