#170818 - 11/12/07 03:13 PM Expansion Fittings
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
This is what happens when the expansion fitting is NOT installed. The side of the box was pulled completely out. These were taken in a parking garage that is being renovated. The metal conduit will probably be replaced by rigid non-metallic conduit sched. 80 WITH expansion fittings.



Quote:
This is the second of two pictures showing an expansion fitting on rigid conduit. This is how it should be done.

Alan Nadon

Top
2017 / 2014 NEC & Related Books and Study Guides
#170907 - 11/14/07 03:45 PM Re: Expansion Fittings [Re: Admin]
BigJohn Offline
Member
Registered: 03/06/04
Posts: 391
Loc: Boston, MA
I understand the reason for expansion fittings, but never really saw an install where I was thinking "They'd really be up a creek if they hadn't put that expansion coupling in." Now here's a dramatic example of what happens when you don't. Neat.

-John
Top
#170918 - 11/14/07 08:44 PM Re: Expansion Fittings [Re: BigJohn]
SP4RX Offline
Member
Registered: 10/01/07
Posts: 56
Loc: Edmonton, Alberta, Canada...eh
Wow.

Is expansion/contraction really what caused that?? I never would have guessed that a lack of provision for expansion could result in something this dramatic.

Kinda makes me ponder the 250 feet or so of EMT I just ran the other day...oh wait, that was inside a heated building. *whew*


Shawn.
Top
#170956 - 11/15/07 04:42 PM Re: Expansion Fittings [Re: SP4RX]
jdevlin Offline
Member
Registered: 08/07/02
Posts: 402
Loc: welland ontario canada
That must have been some long conduit run to expand/shrink what looks like 2 inches. Are you sure it is not from damage further down the conduit run?
Top
#170970 - 11/15/07 09:06 PM Re: Expansion Fittings [Re: jdevlin]
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
There's a run of 3/4 galvanized that runs along a fenceline for about 1200 feet out where I work (For H2S monitors) In the cold, it's straight as an arrow, but once it gets above about 80F or so... It starts doing the wave... along the WHOLE run!
Top
#171132 - 11/20/07 09:43 AM Re: Expansion Fittings [Re: Lostazhell]
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
The coefficient of thermal expansion for steel is 0.00000645in/in/deg. Doesn't sound like much, but for a 100' piece of pipe, the difference between a -20F day and a 110F day is 1". Aluminum expands twice as much as steel. Concrete is practically identical to steel. (Convenient for rebar, eh?) BUT, if that concrete has expansion joints, and the steel doesn't...

PVC is far worse, as it has a much higher coefficient of expansion. A similar piece of RNC would have an appx 4.5" expansion/contraction.


Edited by SteveFehr (11/20/07 09:45 AM)
Top
#182701 - 12/06/08 09:39 PM Re: Expansion Fittings [Re: SteveFehr]
JoeKP Offline
Member
Registered: 03/29/08
Posts: 144
Loc: Berkley, MA
look @ how bent up it is, i don't think an expansion fitting would of helped that
_________________________
-Joe
“then we'll glue em' then screw em'”
-Tom Silva
TOH
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals